For want of a nail....

On Wed, Apr 16, 2008 at 12:27 PM, Charles Thurston
<[EMAIL PROTECTED]> wrote:
> Hello Craig,
>
>  Emergency Pager went off at 6pm one Friday. It turned out to be a customer
>  where we had replaced the jockey pump the day before. His electrician had
>  been out that morning and wired up the new jockey pump and life was good....
>  UNTIL The pump need to run... Well the electrician did not check the
>  voltage the pump was wired for before he hooked it to the 208 3 phase
>  controller, Yup it was still wired for the 440 from the factory. When I saw
>  the jockey pump it was covered in ABC Extinguisher powder where the Fire
>  Department had put the fire out.
>
>  The jockey smoked, The smoke got sucked into a hole the maintenance guy had
>  cut into the duct work for the office AC to keep the pump room cool since
>  it was his shop space also, This set off the building fire alarm, This
>  caused the Fire Department response and they put it out before the fire got
>  any worse.
>
>  The next week we put in another jockey pump and he hired a real electrician
>  to hook that one up.
>
>
>
>  Wednesday, April 16, 2008, 1:53:58 PM, you wrote:
>
>  > But make sure that electrical components (motors especially) are U.L.
>  > labeled.  Some AHJ's do look for that label.  Some of the cheap overseas
>  > knock-off products aren't UL tested or labeled.  It would be real sad to
>  > have a fire in a pump room/house started by one of the fire protection
>  > system components.
>
>  > -----Original Message-----
>  > From: [EMAIL PROTECTED]
>  > [mailto:[EMAIL PROTECTED] On Behalf Of John
>  > Denhardt
>  > Sent: Wednesday, April 16, 2008 1:29 PM
>  > To: sprinklerforum@firesprinkler.org
>  > Subject: RE: Help with jockey pump listing
>
>  > Agree - Jockey pumps or Pressure maintenance pumps as the standard calls
>  > them, do not have to be listed.
>
>  > Hope this helps,
>  > John
>
>  > John August Denhardt, P.E.
>  > Strickland Fire Protection Incorporated
>  > 5113 Berwyn Road
>  > College Park, Maryland 20740
>  > Office Telephone Number:  301-474-1136
>  > Mobile Telephone Number:  301-343-1457
>  > FIRE SPRINKLERS SAVE LIVES
>
>  > -----Original Message-----
>  > From: [EMAIL PROTECTED]
>  > [mailto:[EMAIL PROTECTED] On Behalf Of Roland
>  > Huggins
>  > Sent: Wednesday, April 16, 2008 12:56 PM
>  > To: sprinklerforum@firesprinkler.org
>  > Subject: Re: Help with jockey pump listing
>
>  > this section is addressing the use of other types of FIRE pumps.  The
>  > standard does not identify types of Jockey pumps that you can deviate
>  > from.  They are not required to be listed.  This will be better
>  > clarified in the next edition (based on the outcome of the recent ROP)
>
>  > Roland
>
>  > On Apr 16, 2008, at 6:29 AM, Rod DiBona wrote:
>
>  >> When I look at NFPA #20 section 5.1.2.1 it looks like a jockey pump
>  >> must be listed. I had it in my mind that it didn't. My mind vs the
>  >> standard?
>  >> ...probably not a fair contest but just wanted to check and see if I
>  >> am missing something. Thanks.
>  >>
>  >> Rod DiBona
>  >> Vice President
>  >>
>  > _______________________________________________
>  > Sprinklerforum mailing list
>  > Sprinklerforum@firesprinkler.org
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  > To Unsubscribe, send an email
>  > to:[EMAIL PROTECTED]
>  > (Put the word unsubscribe in the subject field)
>  > _______________________________________________
>  > Sprinklerforum mailing list
>  > Sprinklerforum@firesprinkler.org
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  > To Unsubscribe, send an email
>  > to:[EMAIL PROTECTED]
>  > (Put the word unsubscribe in the subject field)
>  > _______________________________________________
>  > Sprinklerforum mailing list
>  > Sprinklerforum@firesprinkler.org
>  > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  > To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  > (Put the word unsubscribe in the subject field)
>
>
>
>  --
>  Best regards,
>   Charles Thurston                            mailto:[EMAIL PROTECTED]
>   Coastal Fire Protection
>
>
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  Sprinklerforum@firesprinkler.org
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to