Actually, in several counties around Atlanta, the test was also required for 
garden style apartments up to four stories.  You would be surprised that, at 
least in the beginning, a number of projects that had full blown hydraulic 
calculations failed when the bucket test showed them to be incorrect.  Many 
times the main culprit was a water test supplied by the water company that was 
faulty or not up to date.  Which brings me to my point that I have made over 
the years, the "design" of sprinkler systems really involves four major 
decisions by the design engineer and the rest is mostly a layout of a system 
within the rules of the codes.

First Engineering Decision:     What is the hazard and what densities are 
required.  The project must be classified as per the fire risk. What are you 
protecting and how much water will it require to achieve the fire protection 
objective.

Second Engineering Decision:  What is the water supply and has there been a 
detailed analysis and testing of the water supply?  Generally, engineers and 
others rely on water tests provide by others and sometimes incorrect and out of 
date. Often very little time is devoted by the engineer to insure that an 
adequate water supply at the needed pressure is available.  This does not mean 
just throwing in a large fire pump just to be safe.

Third Engineering Decision:  Where is the remote area?  It is easy to just let 
the designer decide but the selection of the remote area can change the 
hydraulics dramatically.

Fourth Engineering Decision:  Coordination and review of the plans. The shop 
drawings and calculations may be checked and the coordination with the other 
trades on the project.  Often, the engineer just passes these functions to a 
trainee or someone else within the engineering firm. In other cases the issue 
is just ignored.

Too often these decisions are not given the time and effort that they deserve.


Michael L. Brown
Manager of Technical Services
The Reliable Automatic Sprinkler Company, Inc.'
[EMAIL PROTECTED]
www.reliablesprinkler.com
(864) 843-5228

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Wednesday, April 23, 2008 8:08 PM
To: [email protected]
Subject: RE: What is a Bucket Test?

Bucket test, IMHO, was to "prove" the "shortcut" calcs allowed under 13D
worked. 13R calcs are done to the same level of care as #13 calcs, so no
bucket test was needed.

In #13D done with shortcut calcs, makes sense and isn't a big deal-
especially when you consider the downside (fire death in sprinklered house).

But flowing 20 heads in a 13 system? Be careful what you ask for is right.

glc


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Thursday, April 10, 2008 12:39 PM
To: [email protected]
Subject: Re: What is a Bucket Test?

Chris,

This silly test tells you nothing that other tests don't already tell
you. It certainly doesn't tell you if your system will work or not
because it presumes that conditions at the moment of the bucket test
reflect the moment of the water availability test. Main drain tests
will tell you if pipe is collapsed or valves are shut. What needs to
be done (and I know this won't happen) is to get the water purveyors
to quit handing out old crap and calling it good today. Thanks for
setting me up for this mini-rant.

Ron Greenman
...at home


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to