I'll second that one.  The majority of specs I see that call for FM approval
are not FM insured.

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Mike Brown (TECH- GVL)
> Sent: Thursday, April 24, 2008 1:03 PM
> To: [email protected]
> Subject: RE: engineering decisions
> 
> Joe
> I realize that but I have seen hundreds of specifications where the
> engineer specs it that way requiring both UL and FM Approval.
> 
> Michael L. Brown
> Manager of Technical Services
> The Reliable Automatic Sprinkler Company, Inc.'
> [EMAIL PROTECTED]
> www.reliablesprinkler.com
> (864) 843-5228
> 
> 
> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Joe Hankins
> Sent: Thursday, April 24, 2008 12:33 PM
> To: [email protected]
> Subject: Re: engineering decisions
> 
> Just remember, it's not possible to meet all FM requirements without FM
> being involved. It can't be done with just a copy of FM Data Sheets.
> 
> Joe
> 
> 
> Mike Brown (TECH- GVL) wrote:
> > Roland
> > This will get you going---As usual the engineer does not want to do
> anything but get paid.
> >
> >  Just write in the spec:
> >
> > ["Sprinkler System as per NFPA 13 and all materials and design shall
> meet UL and FM Approvals.  Contractor shall meet all state and local
> codes.  Contractor shall determine the water supply and all drawings are
> schematic and the co-ordination and/or anything else required is to be
> the responsibility of the contractor."]
> >
> > Have a good day!
> >
> > Michael L. Brown
> > Manager of Technical Services
> > The Reliable Automatic Sprinkler Company, Inc.'
> > [EMAIL PROTECTED]
> > www.reliablesprinkler.com
> > (864) 843-5228
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Roland Huggins
> > Sent: Thursday, April 24, 2008 10:59 AM
> > To: [email protected]
> > Subject: Re: engineering decisions
> >
> > Mike: You need to update (that is reduce) your list.  First expand
> > item 2 to identify the engineer needs to determine IF The water
> > supply is adequate.  I've never understood how an AE team can provide
> > room for a pump and it's associated infrastructure if they don't know
> > one is needed until a subcontractor tells them.  Now break out the
> > chain saw. The Third item is definitely to be thrown out.  How can
> > the EOR identify where the remote area is unless they are drawing
> > lines and circles?  Keep cutting and throw out item 4.  The AHJ
> > blesses the plans and do you really want a third party slowing you
> > down for coordination? Although the engineering job assurance plan
> > has this one listed, it is a contractual thing can implement IF the
> > owner wants it but not a valid requirement.  The exception to this
> > statement are when BUILDINGS are designed on a performance basis that
> > requires specific sprinkler criteria (that can exceed 13).
> >
> > Roland
> >
> > On Apr 24, 2008, at 6:15 AM, Mike Brown (TECH- GVL) wrote:
> >
> >
> >> Actually, in several counties around Atlanta, the test was also
> >> required for garden style apartments up to four stories.  You would
> >> be surprised that, at least in the beginning, a number of projects
> >> that had full blown hydraulic calculations failed when the bucket
> >> test showed them to be incorrect.  Many times the main culprit was
> >> a water test supplied by the water company that was faulty or not
> >> up to date.  Which brings me to my point that I have made over the
> >> years, the "design" of sprinkler systems really involves four major
> >> decisions by the design engineer and the rest is mostly a layout of
> >> a system within the rules of the codes.
> >>
> >> First Engineering Decision:     What is the hazard and what
> >> densities are required.  The project must be classified as per the
> >> fire risk. What are you protecting and how much water will it
> >> require to achieve the fire protection objective.
> >>
> >> Second Engineering Decision:  What is the water supply and has
> >> there been a detailed analysis and testing of the water supply?
> >> Generally, engineers and others rely on water tests provide by
> >> others and sometimes incorrect and out of date. Often very little
> >> time is devoted by the engineer to insure that an adequate water
> >> supply at the needed pressure is available.  This does not mean
> >> just throwing in a large fire pump just to be safe.
> >>
> >> Third Engineering Decision:  Where is the remote area?  It is easy
> >> to just let the designer decide but the selection of the remote
> >> area can change the hydraulics dramatically.
> >>
> >> Fourth Engineering Decision:  Coordination and review of the plans.
> >> The shop drawings and calculations may be checked and the
> >> coordination with the other trades on the project.  Often, the
> >> engineer just passes these functions to a trainee or someone else
> >> within the engineering firm. In other cases the issue is just
> ignored.
> >>
> >> Too often these decisions are not given the time and effort that
> >> they deserve.
> >>
> >>
> >> Michael L. Brown
> >> Manager of Technical Services
> >> The Reliable Automatic Sprinkler Company, Inc.'
> >> [EMAIL PROTECTED]
> >> www.reliablesprinkler.com
> >> (864) 843-5228
> >>
> >>
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> >
> >
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)