Oh, I agree Craig. I was simply referring to an instance when a certain
performance was to be met that was only in the FM guides. For example,
using 1.4 instead of 1.2 to elongate the design area. Or, as another
example, a limitation on water velocity. Simply indicating that FM
guidelines must be met and no reference to the particular FM document.
Additionally, requiring that FM 2.8N be met without really knowing what you
need. The certain things desired in these documents can be added to a
specification without increasing its volume drastically.
Thank You
Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102
[EMAIL PROTECTED]
com To
Sent by: [email protected]
sprinklerforum-bo cc
[EMAIL PROTECTED]
er.org Subject
RE: engineering decisions
04/24/2008 03:39
PM
Please respond to
[EMAIL PROTECTED]
resprinkler.org
It could get quite laborious to regurgitate all the FM data and
specifications for an item when all you have to say is that "XYZ Valve
must be an FM approved device" if you have been directed by an owner or
underwriter to do so. The wordier the specification the less likely it
will be met, keep it simple for everyone.
It's only lazy when you didn't bother to ask if there really is a
requirement for items to be FM approved and you throw the note in just
to cover yourself because you really don't have a clue.
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 24, 2008 4:19 PM
To: [email protected]
Cc: [email protected];
[EMAIL PROTECTED]
Subject: RE: engineering decisions
In my opinion, it is OK to required an FM approved device as these
approvals are published and many devices and items are noted as being FM
approved. However, if we want to require systems or special issues that
are in the FM guidelines, it would be best to simply provide the
specific language in the specifications instead of indicating that it
must meet FM requirements. To simply reference any and all published
guides and standards amounts to lazy engineering.
Thank You
Rahe Loftin, P.E.
Region 7 - GSA
Office - 817-978-7299
Fax - 817-978-8644
Cell - 817-371-3102
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)