Actually 25 says they shall be maintained. It is understood by 25 that they shall be provided.

As already identified 14.1.2 indicates t as well as the CMTC under Plans states Installation conforms to accepted plans.

I doubt that a new set of calculations is performed for a couple of elbows (that's one of the reasons to leave a margin).

Roland

On Apr 27, 2008, at 4:36 PM, Mark Hasenmyer wrote:

Bill:

2006 IFC also references 2002 NFPA-25; see 4.6. NFPA-13 18.1 says that
sprinklers systems must comply with NFPA-25 and NFPA-25 4.6 requires
as-builts.

Mark Hasenmyer, PE
MEH Fire Protection Engineering LLC
1311 River Oaks Drive
Flower Mound, TX 75028
Office (972) 874-2662
Fax (972) 874-5591


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Sunday, April 27, 2008 6:18 PM
To: [email protected]
Subject: RE: As-Built Documentation

2002, referenced by 2006 IBC.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: RE: As-Built Documentation
From: "John Drucker" <[EMAIL PROTECTED]>
Date: Sun, April 27, 2008 12:28 pm
To: <[email protected]>

Which edition ?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Sunday, April 27, 2008 11:10 AM
To: [email protected]
Subject: As-Built Documentation

Would you say NFPA 13 "requires" as-built drawings and calculations?

I know 99.9% of the systems are installed exactly like the shop
drawings. But, for that other 0.1%, is it necessary to do an as-built
calculation to match the as-built drawing? It seems NFPA 13 is based on the 99.5% and is silent about what documentation is required when field
changes occur during installation.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to