Bill, While the applicable codes and standards may not explicitly spell out "as builts" the language of codes and standards gets you to that point where a deviation occurs from the approved plans.
Think about it this way, you submit plans and calcs and receive approval and a permit to install the job. The permit is only valid for the work approved, so a deviation essentially invalidates the permit. Fortunately the code(s) give the code official quite abit of latitude in this area. Check out 2002 NFPA-13 14.1.2, 2006 IBC 901.2, 901.3, 2006 IFC 901.2 and 901.2.1. This position is also supported in NJ pursuant to the NJ Uniform Construction Code, N.J.A.C. 5:23-2.23(i)6. (Certificate Requirements-Application) which states; "A set of amended drawings, if required by the construction official and the appropriate subcode officials when the dimensions, layout or appearance of the building or structure deviates substantially from the released plans and specifications filed with the construction permit application". Hope this helps, John Drucker Fire Protection Subcode Official (AHJ) New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Sunday, April 27, 2008 12:29 PM To: [email protected] Subject: RE: As-Built Documentation Which edition ? -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Sunday, April 27, 2008 11:10 AM To: [email protected] Subject: As-Built Documentation Would you say NFPA 13 "requires" as-built drawings and calculations? I know 99.9% of the systems are installed exactly like the shop drawings. But, for that other 0.1%, is it necessary to do an as-built calculation to match the as-built drawing? It seems NFPA 13 is based on the 99.5% and is silent about what documentation is required when field changes occur during installation. Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)