Sounds like a good solution.

Am I correct in assuming that the tank provider will installing 
installation?  If might be worthwhile to consider increased insulation to 
boost your R-factor.  I've had recent success using a bayonet style 
heater.

James L.(Jim) Roberts, PE/SET
Fluor Corporation
100 Fluor Daniel Drive - C104F
Greenville, SC 29607
864.281.5149
864.281.4916(Fax)





Todd Williams - FPDC <[EMAIL PROTECTED]>
Sent by:  [EMAIL PROTECTED]
05/13/2008 07:14 AM
Please respond to sprinklerforum

To
[email protected]
cc

Subject
Split system







I am working on a chemical storage warehouse. The decision has been 
made to protect it with sprinklers alone and not foam. The total 
water demand for ceiling, in-rack and hose is around 3300 gpm. The 
public supply alone cannot provide this volume. The proposal has been 
made to feed the ceiling sprinklers from a pump and tank and the 
in-racks and hose from the public. Hydraulically that can work. Is 
there any restriction or problem with this type of arrangement? The 
only cross connection between the tank and the public would be in the 
fill line. To me, this would be a more reliable system that feeding 
the entire system from a single pump and tank. This is the first of 
what could be 3 or 4 buildings protected similarly.

While we are at it. This tank will be in the 200,000 gallon range. In 
light of ever-increasing fuel prices, any good suggestions on 
decreasing heating costs?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

------------------------------------------------------------
The information transmitted is intended only for the person 
or entity to which it is addressed and may contain 
proprietary, business-confidential and/or privileged material.  
If you are not the intended recipient of this message you are 
hereby notified that any use, review, retransmission, dissemination, 
distribution, reproduction or any action taken in reliance upon 
this message is prohibited. If you received this in error, please 
contact the sender and delete the material from any computer.  

Any views expressed in this message are those of the individual 
sender and may not necessarily reflect the views of the company.  
------------------------------------------------------------
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to