Thanks Joe, but I'm not using the "room design" method but the "dwelling"
section of the standard and even if I were using the room design method,
11.2.3.1.8(3) states that the 3,000 s.f. area shall be used. Did I
misinterpret what you are saying?

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell
Sent: Thursday, May 15, 2008 4:21 PM
To: [email protected]
Subject: RE: NFPA13 Dwelling vs Mercantile

Commentary from NFPA 13 02'

"Also, if residential sprinklers are used in a dwelling unit and an
unprotected, combustible concealed space exists, the area limitations of
11.2.3.1.8(3) do not apply because the discharge criteria for residential
sprinklers are not based on the density/area method."

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Russell
Sent: Thursday, May 15, 2008 2:01 PM
To: AFSA
Subject: NFPA13 Dwelling vs Mercantile

Again I've come across something I've never dealt with so I am going to need
your help please. Recently there has been discussion concerning the fact
that NFPA13R occupancies cannot be over mercantile occupancies that are not
incidental to the residential occupancy. What I have is a three story
building with mercantile on the ground level. The other two floors above are
apartments. The entire building is designed by NFPA13 standards. The
apartments are designed using the "Dwelling" section of NFPA13. So far I'm
okay I think, but now I find that the floor system for second and third
floor is comprised of "TJI" composite wood joist with the ceilings directly
attached thus creating combustible concealed spaces and requiring the
dreaded minimum 3000 sq. ft. design area. The question is does this now make
the use of NFPA13 "Dwelling" null and void? It would appear to me that it
would, but I need other opinions/rulings.

 

Thanks,

Russell

 


No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.16/1433 - Release Date: 5/14/2008
4:44 PM
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.16/1445 - Release Date: 5/15/2008
7:25 PM
 

No virus found in this outgoing message.
Checked by AVG. 
Version: 7.5.524 / Virus Database: 269.23.16/1445 - Release Date: 5/15/2008
7:25 PM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to