In theory and on paper, sure.  But in reality, can you meter the outflow
from the hydrants to exactly no more than 500 gpm?   Probably not, so if
you can't control the outflow you can't say with any relative certainty
that the tank will fill at a rate of 100 gpm.  

Does the tank only service the hydrants, no sprinkler systems right?




Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dyce
Geoffrey H.
Sent: Thursday, May 22, 2008 9:33 AM
To: [email protected]
Subject: Tanks

Situation.....Flow test shows water flow at 600 gpm at 29 psi Hose
requirement is 500 gpm at the main hydrant System requires 600 gpm for
90 minutes Using a tank, can I say under a flowing situation, the tank
will fill at a rate of 100 gpm because of the hose requirement?
Would I then require a tank based on 500 gpm for 90 minutes or a tank of
45,000 gallons?
Thanks for your help

Geoffrey H. Dyce
Sales Manager
Contractor I, #87582700012007
NICET IV
Industrial Fire & Safety Inc.
Ph:    727-573-1556
Fx:    727-572-7266
Cell:  727-644-8872

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to