Say what ?.  Is there a common corridor or is this four separate
compartments each with their own means of egress to the exterior of the
building without passing through the others and within the non
sprinklered exit access, travel distances, corridor ratings,  ?

Any code references provided in any of this ?

John
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Thursday, May 29, 2008 3:52 PM
To: [email protected]
Subject: RE: partial system

I am not sure exactly what their purpose is.

The chief building inspector says that they do not have to protect the
building at all because the arch. Has compartmentalized the building
into 4
- 3,000 sq ft compartments which kicks them out of the greater than 30
people chart.

The building is classified as "S" btw.

Therefore since sprinklers are not required he is happy with corridor
only.
I of course informed him of the "if you go you have to go all the way"
requirement and he blew me off and there we are. 

We will not do this project as is, I was just trying to get answers
before I stuck my foot in my mouth again.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Thursday, May 29, 2008 1:39 PM
To: [email protected]
Subject: RE: partial system

Is this a means of egress question ?

If so then take a look at the following 2006 IBC Chapter 10 provisions;

1) Exit Access 1014.3 - Exception 1 - "building is equipped THROUGHOUT
with an automatic sprinkler system installed in accordance with Section
903.3.1.1" (NFPA-13-2002)

2) Travel Distance Table 1016.1 Note c. -"buildings equipped THROUGHOUT
with an automatic sprinkler system installed in accordance with Section
903.3.1.1" (NFPA-13-2002)

3) Corridor Fire Resistance Rating Table 1017.1 Note c. -"buildings
equipped THROUGHOUT with an automatic sprinkler system installed in
accordance with Section 903.3.1.1(NFPA-13-2002) or 903.3.1.2
(NFPA-13R-2002) [13R provision not applicable in non residential
buildings]

Does that help ?

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Thursday, May 29, 2008 12:25 PM
To: [email protected]
Subject: partial system

OK, got a architect and engineer that claim that they can protect the
corridors only on a mini-storage warehouse. 
:

The IBC states that if the building has sprinklers but does not say
sprinklered throughout - has anyone else seen/done this?




Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated,
intended to be relied upon by any person or persons other than the
individual or entity named above and no warranties or representations
are made or intended to persons or entities not named above.  If the
reader is not the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited.  If you have received this communication in error, please
notify us immediately by telephone, return this message to the address
above and delete all copies.  Thank you.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to