1. IBC 901.2 allows non-required partial systems if installed properly (and this doesn't mean the system has to be installed throughout the building to be considered installed properly). 2. IBC 508.2.3 allows partial systems in certain areas. 3. NFPA 101A is full of partial systems for various occupancies. 4. IBC Chapter 34 has point values for partial systems.
It would be incorrect to say that you must go all the way with sprinklers if you choose to sprinkler a corridor in a building that does not otherwise require sprinkler protection. Why don't you run the IBC Chapter 34 point values for this building and see if IBC 901.2 can be appropriately applied for the corridor sprinkler system? Maybe the AE has already done this and the attorney's phone number can be put back into the rolodex. Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146 410-544-3620 Phone 410-544-3032 FAX 412-400-6528 Cell -------- Original Message -------- Subject: RE: partial system From: <[EMAIL PROTECTED]> Date: Thu, May 29, 2008 5:23 pm To: <[email protected]> Yeah I'd have to ask them, per WHAT code? Has be NFPA 13, right? lol Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Thursday, May 29, 2008 5:17 PM To: [email protected] Subject: RE: partial system Being right and doing things right is easy to defend. Just write a check and pay the attorney until he works it out. I guess the statement that bothers me is the drawings that says "sprinklers to be provided in corridors only. (per code)" The (per code) gets me. Like you said, I can pass on it but I want to learn. Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Thursday, May 29, 2008 3:54 PM To: [email protected] Subject: RE: partial system What's to defend? The building doesn't require any sprinklers at all. I've yet to see a protected mini-warehouse facility, even those built to be occupied for business purposes adjacent to storage units. If there's still a level of discomfort either pass on the job or put disclaimers on the drawings and bid stating that the sprinkler system does not comply with the intent of XYZ Code and Standards for a fully sprinkled facility and that you as the designer/installer will not guarantee it's function for the protection of the building, it's contents or occupants, blah, blah blah..... Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Thursday, May 29, 2008 4:37 PM To: [email protected] Subject: RE: partial system I understand that, but do I really want to try to defend us in the event of a fire that starts in a non-sprinklered storage unit and overruns the sprinklers in the corridor? Maybe in another type of occupancy; but I have helped people move before and I have seen the partially filled plastic gas cans and lawnmowers, weedeaters and gas grill LP bottles, etc in these units. Scary to me. Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer Sent: Thursday, May 29, 2008 3:22 PM To: [email protected] Subject: RE: partial system Greg, NFPA 13 recognizes that under certain conditions, partial sprinkler systems may be installed as allowed or required by other standards or codes. Section 8.1 and 8.1.1 (07) along with A.8.1 and A.8.1.1 and the commentary in the handbook will give you the details. Ed Kramer Littleton, CO > -----Original Message----- > From: [EMAIL PROTECTED] [mailto:sprinklerforum- > [EMAIL PROTECTED] On Behalf Of Greg McGahan > Sent: Thursday, May 29, 2008 1:52 PM > To: [email protected] > Subject: RE: partial system > > I am not sure exactly what their purpose is. > > The chief building inspector says that they do not have to protect the > building at all because the arch. Has compartmentalized the building > into 4 > - 3,000 sq ft compartments which kicks them out of the greater than 30 > people chart. > > The building is classified as "S" btw. > > Therefore since sprinklers are not required he is happy with corridor > only. > I of course informed him of the "if you go you have to go all the way" > requirement and he blew me off and there we are. > > We will not do this project as is, I was just trying to get answers > before I stuck my foot in my mouth again. > > Thank you, > Greg McGahan > > Living Water Fire Protection, LLC > 1160 McKenzie Road > Cantonment, FL 32533 > 850-937-1850 > Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)