2007, 9.3.6.3 - The end sprinkler on a line shall be restrained against
excessive vertical and lateral movement.

1.  Can I assume the word line means "branch line" based on the title of
9.3.6?
2.  Would the end sprinkler include sprinklers on drops, arm-overs, and
return bends?
3.  Would "excessive" be defined as using a restraint not listed for
vertical and/or lateral movement or not meeting 9.3.6.1(5)?

Someone has asked me to approve a particular brace but then I realized I
had no idea how many needed to be installed!

(Getting old but still learning)
 