Would you be calculating the interior piping for the combined flows of
the exterior streams and interior sprinkler system?  Keeping in mind
that a wall hydrant - if it's a "real" wall hydrant and part of the site
fire flow design - would likely have to discharge 1500 GPM minimum,
perhaps more per the Fire Code.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Wednesday, June 18, 2008 3:57 PM
To: [email protected]
Subject: Wall hydrants

Does a wall hydrant need a dedicated feed from the riser or can it be
fed off an adjacent sprinkler system as long as a PIV control valve is
installed?
I have only designed them with a dedicated feed  but a salesman is
questioning this and I could not find anywhere in NFPA to back it up.