Thanks Steve for the insight. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Thursday, June 19, 2008 11:38 AM
To: [email protected]
Subject: RE: Wall hydrants

Regardless of the specifics, if the AHJ wants a wall hydrant and will
approve the primary and auxiliary water supply arrangement(s) with
combined mains, and if you can calculate an adequate allowance for the
require outside streams, then I can't see why this would be any
different than taking a hose stream allowance at the standpipe on a
combined system.   If the exterior stream demand exceeds the sprinkler
design, then the mains would have to be designed at least for that
higher flow rate, but I wouldn't undertake that design without CLOSE
consultation with the serving fire department.   Because of the
inside/outside nature of this situation, I wouldn't presume it to be
exactly like a combined system, but similar concepts are at work.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Thursday, June 19, 2008 9:18 AM
To: [email protected]
Subject: RE: Wall hydrants

In the past, the AHJ's have only required 250 GPM at the wall hydrant.
This would be combined in at the point of connection to a common system
point.  I think the intent is to provide an outside hose connection for
the FDP when it is impractical / impossible to get their pumper truck to
this location.  
Dewayne    

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Thursday, June 19, 2008 10:31 AM
To: [email protected]
Subject: RE: Wall hydrants

Would you be calculating the interior piping for the combined flows of
the exterior streams and interior sprinkler system?  Keeping in mind
that a wall hydrant - if it's a "real" wall hydrant and part of the site
fire flow design - would likely have to discharge 1500 GPM minimum,
perhaps more per the Fire Code.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Wednesday, June 18, 2008 3:57 PM
To: [email protected]
Subject: Wall hydrants

Does a wall hydrant need a dedicated feed from the riser or can it be
fed off an adjacent sprinkler system as long as a PIV control valve is
installed?
I have only designed them with a dedicated feed  but a salesman is
questioning this and I could not find anywhere in NFPA to back it up.
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to