I don't believe the intent was to restrain the individual armovers, as their
short length usually will not allow them the motion we're trying to
prevent.(Perhaps the TC could provide a maximum length of armovers, vs.
single head branchlines.) But the branchline they are attached to must be
restrained, and if they are on a crossmain or feed main, those are already
"Braced" a higher level of restraint.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, June 19, 2008 10:13 AM
To: [email protected]
Subject: Re: Restraint of Branch Lines

There was a proposal (13-283) to require restraint on drops greater than 10
ft which the TC rejected.

Roland

On Jun 19, 2008, at 9:01 AM, Roland Huggins wrote:

> Having said that, I have given up on trying to say what any large 
> group will ultimately decide (that being the technical committee) 
> until it's done.  I will look to see if there is a proposal that we 
> can attach a comment that will clarify this issue come the Sept ROC 
> meeting.
>
> Roland

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to