Roland,
But it is not an arm-over if it is a horizontal pipe (not a return bend,
drop or sprig) fed from a cross main...it is, by definition, a branch line.
You must restrain it if it is required to have a hanger.
Bobby Gillett
Project Manager
[EMAIL PROTECTED]
(731)-424-0130
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Thursday, June 19, 2008 11:01 AM
To: [email protected]
Subject: Re: Restraint of Branch Lines
so would you restrain one and not the other? I still think the
restraint does not apply to an arm-over regardless if it is tied
directly to a cross main or a branch line. Short is short (or should
I say vertically challenged?).
Having said that, I have given up on trying to say what any large
group will ultimately decide (that being the technical committee)
until it's done. I will look to see if there is a proposal that we
can attach a comment that will clarify this issue come the Sept ROC
meeting.
Roland
On Jun 19, 2008, at 8:41 AM, Steven P. Biship, P.E. wrote:
>> So if you have a single sprinkler fed from a horizontal pipe from a
>> cross
>> main this would be a branch line. If you have a single sprinkler
>> fed from
>> a
>> horizontal pipe from a branch line this would be an arm-over.
>>
>>
>> Bobby Gillett
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)