Joe,
Thanks for the response. To give you a little more detail, the shelf units are 
approximately 14" deep by 4' wide with 5 shelves high to 6'. The shelving is 
all sheet metal with solid backs and ends. The shelves are arranged in rows, 
back to back, and share a common divider, (like double row racks without a 
longitudinal flue). They have 4' aisles and are open on the top shelf. This 
storage arrangement occupies an area of about 150,000 square feet in a building 
that encloses 500,000 square feet. There are 2 X 4 foot light fixtures, AC 
ductwork up to 26 inches in diameter and banks of conduit up to 3" in diametter 
and over 2' wide through-out the ceiling space of this building. 
To clarify your second paragraph, when you refer to "meet the obstruction 
rules", I assume you mean these obstructions at the roof, as I have just 
discribed, and not the shelves themselves?
Thanks again, 
Mark at Aero 


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Joe
Hankins
Sent: Friday, June 20, 2008 7:21 PM
To: [email protected]
Subject: Re: ESFR Sprinklers over 8' library shelves


Mark,

First and foremost, this is  an application  that (due to what I presume 
are solid shelves) takes advantage of  none of ESFRs strengths but is 
subject to all of their weaknesses.  Unless these shelves are in a small 
area of a facility that is otherwise a good fit with ESFRs, ESFRs are 
the wrong choice.

If the ESFR protection is already existing and the shelves meet all 
definitions of shelf storage, then you are OK as long as you meet the 
obstruction rules.

The bottom line is that, in order for suppression to reliably occur, you 
have to meet the obstruction rules, regardless of storage height. While 
lowering the storage height makes a fire easier to suppress, increasing 
the clearance makes it harder. The solid shelves further exacerbate the 
challenge.

Joe




Phelps, Mark wrote:
> Mr. Joe Hankins, If you are on line, could you comment on the application of 
> ESFR (K14 at 75 PSI) installed below a 40' high roof protecting class I thru 
> IV misc storage on library style shelves (not an actual library). My specific 
> question is, " do all of the design requirements and obstruction requirements 
> (conduit banks, lights, ducts, etc.) and exceptions apply equally as if it 
> were double row racks of I thru IV stored to 30'? 
> Mark at Aero
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to