We've run into them just south of PA. The AHJ complies with the "no visible
leakage" portion of the code and takes a flashlight up into the attic, walks
around looking at every joint, THEN the drywall can go up......

I offered 48 hours at 250 PSI after the drywall, assuming any leaks would
become obvious on the sheetrock, but no, that or just looking at gauge
pressure weren't enough. Same jurisdiction tried to get us to do a full
hydro for some armovers, which would have exposed an operating MRI and other
big dollar items to a needless hydro risk- on a shell system installed by
others. Took intervention from above, but we finally did our static test and
the AHJ responded by not signing our test paper- but he did sign the C of O.

George Church
Rowe Sprinkler 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
Sent: Monday, July 14, 2008 4:48 PM
To: [email protected]
Subject: Rough-in inspections

Any AHJ's requiring 200 psi hydrostatic tests to be done during the rough-in
inspection?  Not really a problem with ACT ceilings.  Certainly ties things
up in vertical residential systems where you can't zone it.  

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [EMAIL PROTECTED]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to