I've left this pretty much alone, but since Ray has already alluded to
over-thinking the process, I figured I should jump in now because that's
generally something I do very well.  Not as well Roland actually, but
he's been quiet on this thread ...   

Not that this is on-topic specifically, but don't overlook those
situations where the FDC serves a combined sprinkler/manual wet
standpipe system.  In those cases, it might be considered a secondary
water supply for automatic sprinklers, but as the primary water supply
for the standpipe system, its location, functionality, etc. are of the
utmost importance.

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Friday, July 18, 2008 11:40 AM
To: [email protected]
Subject: RE: FDC Connection

Item #2 is wrong it will not "augment or assist". The check valve in the
FDC line will not open until there is a greater pressure on the inlet
side than on the system side.

Ron Fletcher

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ray Vance
Sent: Friday, July 18, 2008 11:30 AM
To: [email protected]
Subject: RE: FDC Connection

After careful deliberation and reflection on all the previous posts to
this thread, it seems to me we may be over-thinking the whole process.

Since the FDC is "supplemental" to the water supply and is not intended
nor required to provide a specifice flow, then the whole concept of
where and how to tie it in becomes a much more simple process.

(1) The FDC connection is a "Parallel" connection, and as such the water
and pressure provided is really nothing more than a MANUAL secondary
supply.
(2) As a "Parallel" supply it will augment or assist the primary supply
until which time as the PRESSURE from the secondary supply exceeds the
primary.
(3) Since it is a MANUAL supply, once the secondary exceeds the primary
it in effect BECOMES the primary, unless manually throttled back to
balance the primary supply pressure.
    No real difference than (2) fire pumps in parallel.
(4) The FDC connection piping size only needs to be as large as the
riser up to the point it connects to the system piping.
    If you calculate a system and need a 4" riser, but reduce the feed
main to 3" from the top of the riser out to the system cross-main, then
what does it matter if the 4" FDC connection piping connects
    to a 3" cross-main? The FDC connection piping, again, in effect,
becomes a 4" riser (without the control valve) until it ties in to the
sytem. (NO DIFFERENCE)
(5) The new position of the NFPA technical committee to connect to
cross-main or feed-mains only (no branch-lines)was made, in my opinion,
to alleviate the inherent difficulties in overcoming extreme
    pressure losses due to both friction and velocity in smaller sized
piping, (2" and smaller) when pumping higher flows at higher pressures,
such as an FDC would provide from a pumper truck.
(6) By limiting the connection to cross-main or feed-mains, the whole
function of the FDC secondary supply overcoming and then BECOMING the
primary supply is addressed, as you will not get the extreme
    pressure losses at higher flows, as you would in 2" or smaller
branch-lines.
(7) At any time the FDC supply pressure drops back below the original
primary supply pressure, the whole process reverts back to the origianl
primary supply.

In my humble opinion, the NFPA standards relating to FDC connections, as
written, already address MOST all the scenarios and issues discussed
this fine Friday afternoon.
With a little more thought process and understanding of the function of
the FDC connection and its purpose, the whole point of "Where to tie it
in", What size it needs to be", "Why tie-in only on feed or
cross-mains", etc, becomes a much clearer picture.

One final thought... Is is quitting time yet ;-)

Ray Vance
Chief Engineering Tech.
Wayne Automatic Fires Sprinklers, Inc.
www.waynefire.com



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Friday, July 18, 2008 1:40 PM
To: [email protected]
Subject: RE: FDC Connection

Flow and pressure cannot be supplemented (boosted) given the valve
arrangement required by NFPA. The main riser check valve is either open
or closed. The handbook calls it an "auxiliary water supply" to the
system. Supplementing the automatic supply and increasing overall
reliability. I have run into a lot of AHJ's that think the FDC will add
to the flow and pressure from the city supply like a booster pump but it
will not. The FDC becomes the sole source of water and pressure when
used.

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, July 18, 2008 9:59 AM
To: [email protected]
Subject: RE: FDC Connection

YES! SUPPLEMENTAL! As stated in NFPA 13, 2007 handbook A.6.8.1

You can do whatever you want thru those 2-2-1/2" connections, but
somehow I don't think they were ever intended to "Supply" the entire
demand for an ESFR 40' warehouse, or a .3/3000 design area, or a large
deluge at a refinery, or--or---or--.

If you do that dangerous thing (use Logic) we should only rely on
2-2-1/2"
connections for up to 500 GPM. (See NFPA 14) Obviously you can, with the
right pumper, and the right hydrant, flow more than 500 at an elevated
pressure. But if it was the intent to "Supply" the entire system demand
through the FDC, why are we not required to prove it? With a hyd. Calc.
using the nearest hydrant and the smallest pumper or responding engine,
and appropriate hose and friction loss? You really want to go down that
path?

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Friday, July 18, 2008 9:05 AM
To: [email protected]
Subject: RE: FDC Connection

Supplemental? If 150 psi is pumped into the FDC the riser check will
close making the FDC the only supply.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, July 18, 2008 7:45 AM
To: [email protected]
Subject: RE: FDC Connection

I think it's important to remember that the FDC is "supplemental" to the
supply, not "Equal" to a supply. I feel that the 4" tied to the 2-1/2"
MAIN
meets the intent of the standard. It does not need to be 4" all the way
from the riser to the FDC, when the FDC is remote from the riser and
connects to a MAIN.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Garth W.
Warren
Sent: Friday, July 18, 2008 9:38 AM
To: [email protected]
Subject: Re: FDC Connection

it should be 4" from the connection to the main and then connected
through a
21/2x21/2x4 tee.  I disagree that NFPA allows for connection anywhere on
the system, it states "provided the pipe size meets the requirements of
8.17.2.3."  Otherwise "creative" companies would have 1" fdc piping
connected to the end of a line.

Garth
----- Original Message -----
From: "Brian Harris" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, July 18, 2008 9:02 AM
Subject: RE: FDC Connection


> The FDC is actually remote from the riser & ties into a 2-1/2"
floating
> main. I think it should at least be 4" all the way to the back main
and
then
> reduce it there....
>
>
> Brian Harris
> FDFP INC.
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of
> [EMAIL PROTECTED]
> Sent: Friday, July 18, 2008 8:48 AM
> To: [email protected]
> Subject: Re: FDC Connection
>
> NFPA 13, 2007, section 8.17.2.3, (3) - For hydraulically calculated
systems,
> the fire department connection shall be permitted to be less than
> 4 in. and no less than the size of the system riser, where serving one
> system riser.
>
> My opinion is that the pipe from the FDC itself to the riser needs to
be
4"
> minimum.  Based on your description I would interpret that as saying
that
> the 2 1/2" pipe on the FDC is not permitted as the riser is 4" and I
am
> assuming the 2 1/2" reduction is between the FDC and the riser.
>
> My opinion only.
>
> Andrew Weisfield
>
>
>
>
> "Brian Harris" <[EMAIL PROTECTED]> Sent by:
> [EMAIL PROTECTED]
> 07/18/2008 08:36 AM
> Please respond to
> [email protected]
>
>
> To
> <[email protected]>
> cc
>
> Subject
> FDC Connection
>
>
>
>
>
>
> Forum,
> Quick FDC connection, I just saw on some drawings that came in that
the
> FDC
> is 4" with a 4" check valve and then reduced down to 2-1/2" with a
> reducing coupling. The system riser is 4", can you choke it down like
> that?
> Technically the FDC is the same size as the riser but where do you
draw
> the
> line? I'm not liking it, what say you???
>
>
> Regards,
>
>
> <http://www.firstdefensefire.com/>
>
>
>
>
>
>
>
>
> E-mail message checked by Spyware Doctor (6.0.0.354) Database version:
> 5.10290e http://www.pctools.com/en/spyware-doctor-antivirus/
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
>
> This email is intended for named recipients only.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>
>
>
>
> E-mail message checked by Spyware Doctor (6.0.0.354) Database version:
> 5.10290e http://www.pctools.com/en/spyware-doctor-antivirus/
>
>
>
>
>
> E-mail message checked by Spyware Doctor (6.0.0.354) Database version:
> 5.10290e http://www.pctools.com/en/spyware-doctor-antivirus/
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.138 / Virus Database: 270.5.1/1559 - Release Date:
7/17/2008
6:08 PM



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.138 / Virus Database: 270.5.1/1559 - Release Date:
7/17/2008
6:08 PM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

-----------------------------------------------------------------------
    Wayne Automatic Fire Sprinklers, Inc.
2006 Inductee into 'The Players Hall of Fame'
       at The Great Games of Business
          http://www.greatgame.com
   Wayne Automatic Fire Spinklers, Inc.
          'Best Places to Work'
       http://tinyurl.com/ov335
      by Orlando Business Journal
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to