See NFPA 13: 11.2.3.2.7.1 the next section below the #30% increases. It tells you to compound the adjustments. 1500 + 30%= 1950, 1950 + 30%= 2535.
Duane Fox, Jr., CFPS, CFI Asst Chief, Technical Services DE State Fire Marshal's Office -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Hasenmyer Sent: Monday, July 21, 2008 9:21 AM To: [email protected] Subject: RE: Increasing Area of Operation 2535; you do one step at a time. Mark Hasenmyer, PE MEH Fire Protection Engineering LLC 1311 River Oaks Drive Flower Mound, TX 75028 Office (972) 874-2662 Fax (972) 874-5591 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Monday, July 21, 2008 8:05 AM To: [email protected] Subject: Increasing Area of Operation Forum, I know it's Monday but I have a really strange question: I have a dry system in an attic with a roof pitch of 5.5 in 12. Per code I need to increase the area of operation 30% for the dry system and another 30% for the roof pitch. I'm fine with that, but which answer is the right one? 1500 + 30% + 30% = 2535 OR 1500 + 60% = 2400 ???????? It's gonna be a long week.... Regards, <http://www.firstdefensefire.com/> E-mail message checked by Spyware Doctor (6.0.0.354) Database version: 5.10290e http://www.pctools.com/en/spyware-doctor-antivirus/ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)