See NFPA 13: 11.2.3.2.7.1 the next section below the #30% increases.  It
tells you to compound the adjustments.  1500 + 30%= 1950, 1950 + 30%=
2535.

Duane Fox, Jr., CFPS, CFI
Asst Chief, Technical Services
DE State Fire Marshal's Office

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Hasenmyer
Sent: Monday, July 21, 2008 9:21 AM
To: [email protected]
Subject: RE: Increasing Area of Operation

2535; you do one step at a time.

Mark Hasenmyer, PE
MEH Fire Protection Engineering LLC
1311 River Oaks Drive
Flower Mound, TX 75028
Office (972) 874-2662
Fax (972) 874-5591


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian
Harris
Sent: Monday, July 21, 2008 8:05 AM
To: [email protected]
Subject: Increasing Area of Operation

Forum,
I know it's Monday but I have a really strange question: I have a dry
system
in an attic with a roof pitch of 5.5 in 12. Per code I need to increase
the
area of operation 30% for the dry system and another 30% for the roof
pitch.
I'm fine with that, but which answer is the right one? 1500 + 30% + 30%
=
2535 OR 1500 + 60% = 2400 ???????? It's gonna be a long week....
 

Regards,

 
<http://www.firstdefensefire.com/>  

 

 




E-mail message checked by Spyware Doctor (6.0.0.354)
Database version: 5.10290e
http://www.pctools.com/en/spyware-doctor-antivirus/

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to