Brian, The increases are COMPOUNDED in that you take 1500 sq.ft. x 1.30 (increase 30%) to 1950 sq.ft. then multiply the result by another 30% (1950 x 1.30) to get to 2535 sq.ft. Since both the slope and the dry system can cause delays in the discharge of water from the sprinklers over the fire area, you must compound the multipliers.
Ray Vance Chief Engineering Tech. Wayne Automatic Fire Sprinklers, Inc. www.waynefire.com<http://www.waynefire.com> ________________________________ From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Monday, July 21, 2008 9:05 AM To: [email protected] Subject: Increasing Area of Operation ----------------------------------------------------------------------- Wayne Automatic Fire Sprinklers, Inc. 2006 Inductee into 'The Players Hall of Fame' at The Great Games of Business http://www.greatgame.com Wayne Automatic Fire Spinklers, Inc. 'Best Places to Work' http://tinyurl.com/ov335 by Orlando Business Journal _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)