Try table 8.6.2.2.1(d). Joseph C. Stough SET, CFPS Tilley Fire Equipment Co. Tel. 215-345-8066 X22 Fax: 215-345-9357 [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]>
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] Behalf Of Russell Sent: Tuesday, August 05, 2008 5:16 PM To: [email protected] Subject: RE: New topic Well, classifying the stored item only gives me the Class 1 ,2, etc. but I do not see anywhere that the class is associated with a particular sprk. s.f. like Class 1, with double row racks less than twenty feet high, non-encapsulated, no in-rack sprk. I don't have a specific project but rather an ahj wanting to see it in the standard. All I can find that states anything pertaining to sprk. s.f. is not in the section pertaining to storage. Only for light, ordinary, extra hazard and other than standard sprk. such as large drop or ESFR. Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [EMAIL PROTECTED] "You need to provide a bit more info. When dealing with storage occupancies you need to clarify what is being stored, how it's being stored (racks, shelves, bins, on floor, pallets), in what type of container (box, crate, tote, jars, etc.), encapsulated, heights of said commodities, etc. Once you've established the what, where, and how then you can go deeper into 13 and find how the area is classified. For some commodities it could be spacing of 130 sq. ft, for others it could be limited to 100 sq. ft. Storage takes some analysis to determine what the appropriate approach will be." _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)