"Almost concealed"? Almost only counts in horseshoes and nuclear war. Now concealed spaces?

At 02:47 PM 8/5/2008, you wrote:
okay, I'll add more fuel to this pile.
Check out the 2009 Report on Proposals, Item 13-210, for a new paragraph
8.15.22.3, which it appears that the committee "accepted in principle".

This would allow for a "largely" unsprinklered noncombustible space
above a lower ceilings of an office or retail sales area...and the space
above the ceiling doesn't even have to be "cut-off" from the storage
areas. Sprinklers are required below the ceiling, but the sprinklers at
the high roof would only extend into a portion of the space above the
ceiling. The proposal even calls this an "almost concealed" space.

I personally don't agree with this proposal, but it on the books for
discussion.
rick matsuda
city of dallas
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to