I checked the archives and couldn't find anything regarding this specific issue.

I've got a 3'-0" overhang with combustible construction.  The attic space has 
18" of insulation with insulation stops at the edge of the building so the 
soffit (overhang) space is open for venting.  The attic space is sprinklered  
(13 system).  Under the overhang is not required to be sprinklered because it 
is less than 4'.

What is typically done with the space in the overhang?  It is a fairly small 
space but wouldn't fall under the criteria of 8.15.1.2.3 for omission.  I 
couldn't find anything in 8.15 that would allow omission of sprinklers in this 
space.

Talking with the architect I found out that this combustible space is always 
ignored in his experience.  It seems as though this scenario would be fairly 
common so I'm looking for how you handle it.

Thanks.