8.15.7.3 (2) 2007 These areas always seem to be ignored in my experience
also. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Reed Roisum
Sent: Monday, August 18, 2008 3:41 PM
To: '[email protected]'
Subject: Combustible Overhang

I checked the archives and couldn't find anything regarding this specific
issue.

I've got a 3'-0" overhang with combustible construction.  The attic space
has 18" of insulation with insulation stops at the edge of the building so
the soffit (overhang) space is open for venting.  The attic space is
sprinklered  (13 system).  Under the overhang is not required to be
sprinklered because it is less than 4'.

What is typically done with the space in the overhang?  It is a fairly small
space but wouldn't fall under the criteria of 8.15.1.2.3 for omission.  I
couldn't find anything in 8.15 that would allow omission of sprinklers in
this space.

Talking with the architect I found out that this combustible space is always
ignored in his experience.  It seems as though this scenario would be fairly
common so I'm looking for how you handle it.

Thanks.


Reed A. Roisum, CET
Fire Protection Technician
NICET Level III

Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079

Direct Number: 701.280.8580
Mobile: 701.212.8810
Main Office: 701.280.8500

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to