As much as a rant against double-interlock pre-action valves in
computer rooms a freezer IS a place that double-interlock makes sense.
You may wish to look into this.

On Mon, Aug 25, 2008 at 2:23 PM, Paul Pinigis <[EMAIL PROTECTED]> wrote:
> Yes, you can grid a single-interlock pre-action system.  But, in your
> case, the specific requirements for Large Drop Sprinklers take precedent
> over the general rules.  So, you must design the system as though it
> were a dry-pipe system (not gridded, C=100, 40% area increase, etc.)
>
> Paul J. Pinigis, P.E.
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Jimmy
> Waite
> Sent: Tuesday, August 19, 2008 6:48 PM
> To: [email protected]
> Subject: * Possible Spam *Pre-Action C Value
>
> Good afternoon everyone,  I am confused by some seemingly conflicting
> wording about single-interlock pre-action systems and I need some help.
>
>
>
>
> Here is the situation.  We are protecting a warehouse with Large Drop
> Heads.
> There is a cooler, and a separate Freezer.  They are storing up to 16
> feet,
> with a ceiling at 20 feet in these spaces.  We are protecting this space
> with a Single-Interlock Pre-Action system with Large Drop Heads.  Here
> is
> where I am getting confused.  All code references are in the 2002
> edition.
>
>
>
> 7.3.2.5 - Double Interlock systems can't be gridded.  (So I can grid by
> Single-Interlock)
>
> 12.3.2.2.5- (A) Consider the pre-action systems dry  (Table 12.3.2.2.1
> (b)
> is the appropriate table)
>
>                      (B) When the detection system activating the
> preaciton
> system will cause water to be at the sprinklers when they operate,
> preaction
> systems shall be permitted to be treated as wet pipe systems.
>
> Table 14.4.4.5 - Black Steel (dry systems including preaction) C Value
> of
> 100; Black Steel (wet system including deluge) C Value of 120.
>
>
>
> SO, Is my Single-Interlock Preaction protecting the Cooler and Freezer a
> wet
> system that I calculate with a C Value of 100?  This just seems very odd
> to
> me and doesn't make much sense.  OR, since 12.3.2.2.5 (b) says by system
> is
> wet, I calculate it with a C Value of 120?  Please help me sort this
> out.
>
>
>
> Also, as a side note, is there any language that will let me eliminate
> hose
> stations (in the 2002 edition) in a warehouse, storing up to 20 feet,
> with a
> ceiling of 28 feet, containing a class 4 commodity on open shelf,
> multiple-row racks?
>
>
>
> Thank you all in advance for your time and comments.
>
>
>
>
>
>
>
> Jimmy Waite
>
> Burtell Fire Protection, Inc.
>
> [EMAIL PROTECTED]
>
> (406) 652-7697
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to