Tom et al, This is a device that was designed and listed for dry pipe valves only. Digging through a bunch of old literature to locate a cut sheet for this device was a bit of a challenge, however we still have one. Send me note off line if you would like a copy. The spec sheet is date 3/70 which is March of 1970 and I am quite sure it is not the first release.
Based on all of that, the WFTA is at least 40 years old. There are a lot of moving parts in that device and if the McCulloh portion is not needed for the system and you are experiencing problems, I would recommend replacing the device. A water flow pressure switch is what you need and piping to change the direction 90 degrees so a female pipe fitting is pointing up. The basic operation is a bellows that moves as the pressure increases against spring tension (the pressure setting of 4-8 psi). As the bellows moves, a lever sweeps and activates the switches. There are no parts still available from the original manufacturer. Best guess is we quite producing those somewhere in the mid to late 80's. We found a 1983 catalog with the WFTA still in it. Hope this helps some. Kind Regards, Tim Frankenberg Tim Frankenberg, CFPS CT Fire Product Manager Potter Electric Signal Company LLC 2081 Craig Road St. Louis, MO 63146 www.pottersignal.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Ed Vining Sent: Monday, September 08, 2008 2:26 PM To: [email protected] Subject: Re: Testing... Yeah, that is what i thought it was. I expect you found them on dry systems, or sitting on top of retard chambers on wet systems. It is a pressure operated McCulloh transmitter. You should find apiece with four arms, one of which looks like a small tuning fork. Unless someone has already done it, you don't want to mess with the relative positions of these arms. A long arm rests on the zinc-looking wheel. The "tuning fork" is what allows the mechanism to run, and stop. One of the short arms should be located such that it is affected by the pressure gadget. The bellows should move the pressure gadget in and out when pressure is applied and released. I think the pressure required was about 15 psi. The transmitter should cause the code wheel to rotate four times for alarm, and one time for restoration. Mechanism speed is controlled by weights on the Geneva escapement. Perhaps the return spring on the bellows is set too low. Maybe the orifice is plugged. Or perhaps there is an adjustment controlling the thingy the short arm rests on. Ed On Mon, Sep 8, 2008 at 11:17 AM, Tom Duross <[EMAIL PROTECTED]> wrote: > It's about 8x8x4 with a 1/2" pressure tap in the rear. > It's got a wind up coil spring like Grampy's old wall clock. > It uses the old Potter T handled round wrenches with the 2 tabs to open and > wind it. > There are 2 nuts you can take off to get to wind it without taking off the > cover (which I learned AFTER taking off the cover). > It's got notched wheels like the old coded alarm transmitters that control > a > telegraph style contacts that tap according to the notches on the wheels. > Really interesting thing, looked like a Gamewell but it was a Potter. I > emailed them about it. > I tested a building last week with three of them, one on each system. > Two seemed to work, they signal alarm and then reset. One wouldn't reset. > I suggested they let me install vane switches so I can take these home and > play with them. :) > Anybody ever seen one? > > Tom Duross > FGOL > GRS > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] Behalf Of Ed Vining > Sent: Monday, September 08, 2008 11:46 AM > To: [email protected] > Subject: Re: Testing... > > > Don't remember it, Tom. > > Is this a pressure operated transmitter, with a Plumb movement and no > retard? > > If so, I think I can dig up a Plumb movement for you. > > Ed > > On Mon, Sep 8, 2008 at 7:04 AM, Tom Duross <[EMAIL PROTECTED]> wrote: > > > Are we working? > > > > Anyone ever repair an old Potter WFTA switch? > > > > Tom > > _______________________________________________ > > Sprinklerforum mailing list > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: > [EMAIL PROTECTED] > > > > To Unsubscribe, send an email > to:[EMAIL PROTECTED]<to%3ASprinklerforum-request@ firesprinkler.org> > <[EMAIL PROTECTED] > sprinkler.org> > > (Put the word unsubscribe in the subject field) > > > > > > -- > Ed Vining > 4819 John Muir Rd > Martinez CA 94553 > 925-228-8792 > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [EMAIL PROTECTED] > > To Unsubscribe, send an email to:[EMAIL PROTECTED]<to%3ASprinklerforum-request@ firesprinkler.org> > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [EMAIL PROTECTED] > > To Unsubscribe, send an email to:[EMAIL PROTECTED]<to%3ASprinklerforum-request@ firesprinkler.org> > (Put the word unsubscribe in the subject field) > -- Ed Vining 4819 John Muir Rd Martinez CA 94553 925-228-8792 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)