Tom et al,

This is a device that was designed and listed for dry pipe valves only.
Digging through a bunch of old literature to locate a cut sheet for this
device was a bit of a challenge, however we still have one. Send me note
off line if you would like a copy. The spec sheet is date 3/70 which is
March of 1970 and I am quite sure it is not the first release. 

Based on all of that, the WFTA is at least 40 years old. There are a lot
of moving parts in that device and if the McCulloh portion is not needed
for the system and you are experiencing problems, I would recommend
replacing the device. A water flow pressure switch is what you need and
piping to change the direction 90 degrees so a female pipe fitting is
pointing up. 

The basic operation is a bellows that moves as the pressure increases
against spring tension (the pressure setting of 4-8 psi). As the bellows
moves, a lever sweeps and activates the switches. There are no parts
still available from the original manufacturer. 

Best guess is we quite producing those somewhere in the mid to late
80's. We found a 1983 catalog with the WFTA still in it.

Hope this helps some.

Kind Regards,

Tim Frankenberg

Tim Frankenberg, CFPS CT
Fire Product Manager
Potter Electric Signal Company LLC
2081 Craig Road
St. Louis, MO 63146
www.pottersignal.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Vining
Sent: Monday, September 08, 2008 2:26 PM
To: [email protected]
Subject: Re: Testing...

Yeah, that is what i thought it was.  I expect you found them on dry
systems, or sitting on top of retard chambers on wet systems.

It is a pressure operated McCulloh transmitter.  You should find apiece
with
four arms, one of which looks like a small tuning fork. Unless someone
has
already done it, you don't want to mess with the relative positions of
these
arms.  A long arm rests on the zinc-looking wheel.  The "tuning fork" is
what allows the mechanism to run, and stop.  One of the short arms
should be
located such that it is affected by the pressure gadget.  The bellows
should
move the pressure gadget in and out when pressure is applied and
released.
I think the pressure required was about 15 psi.  The transmitter should
cause the code wheel to rotate four times for alarm, and one time for
restoration.  Mechanism speed is controlled by weights on the Geneva
escapement.

Perhaps the return spring on the bellows is set too low.  Maybe the
orifice
is plugged.  Or perhaps there is an adjustment controlling the thingy
the
short arm rests on.

Ed

On Mon, Sep 8, 2008 at 11:17 AM, Tom Duross <[EMAIL PROTECTED]>
wrote:

> It's about 8x8x4 with a 1/2" pressure tap in the rear.
> It's got a wind up coil spring like Grampy's old wall clock.
> It uses the old Potter T handled round wrenches with the 2 tabs to
open and
> wind it.
> There are 2 nuts you can take off to get to wind it without taking off
the
> cover (which I learned AFTER taking off the cover).
> It's got notched wheels like the old coded alarm transmitters that
control
> a
> telegraph style contacts that tap according to the notches on the
wheels.
> Really interesting thing, looked like a Gamewell but it was a Potter.
I
> emailed them about it.
> I tested a building last week with three of them, one on each system.
> Two seemed to work, they signal alarm and then reset.  One wouldn't
reset.
> I suggested they let me install vane switches so I can take these home
and
> play with them.  :)
> Anybody ever seen one?
>
> Tom Duross
> FGOL
> GRS
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] Behalf Of Ed
Vining
> Sent: Monday, September 08, 2008 11:46 AM
> To: [email protected]
> Subject: Re: Testing...
>
>
> Don't remember it, Tom.
>
> Is this a pressure operated transmitter, with a Plumb movement and no
> retard?
>
> If so, I think I can dig up a Plumb movement for you.
>
> Ed
>
> On Mon, Sep 8, 2008 at 7:04 AM, Tom Duross <[EMAIL PROTECTED]>
wrote:
>
> > Are we working?
> >
> > Anyone ever repair an old Potter WFTA switch?
> >
> > Tom
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
> [EMAIL PROTECTED]
> >
> > To Unsubscribe, send an email
>
to:[EMAIL PROTECTED]<to%3ASprinklerforum-request@
firesprinkler.org>
> <[EMAIL PROTECTED]
> sprinkler.org>
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ed Vining
> 4819 John Muir Rd
> Martinez CA 94553
> 925-228-8792
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
[EMAIL PROTECTED]
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]<to%3ASprinklerforum-request@
firesprinkler.org>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to:
[EMAIL PROTECTED]
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]<to%3ASprinklerforum-request@
firesprinkler.org>
> (Put the word unsubscribe in the subject field)
>



-- 
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-8792
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to