Pardon me. I work in the Cleveland Ohio area where Lake Erie (but not a good NFL team) is handy. It's not hard to determine flow direction, as the Cleveland Water Department furnishes
the pumping station source.

Regarding circulating mains, the larger size usually supplies the smaller size. And no, it shouldn't because you'll extend your calcs to the test point, right?

At 10:29 AM 9/23/2008, you wrote:
I agree with flowing the hydrant closets to the tap, but how do you tell
which way is upstream or downstream? This particular site utility drawing
limited at best, it shouldn't make that big of a difference should it?


Brian Harris

Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730 F 440 572-7719 Email: <mailto:[EMAIL PROTECTED]>[EMAIL PROTECTED]