I would flow the hydrant closest to where the run-in to the building will
be, in general, and put the residual gage upstream of that.
Bill Minkel,
Sprinkler DesignerMember
NFPA
Dallas, TX
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Tuesday, September 23, 2008 9:13 AM
To: [email protected]
Subject: Flow Hydrant vs. Test Hydrant
O.K., can someone please help a dummy out (that would be me)? When looking
at a Civil Site Utility plan what method do you use to determine which
hydrant you want to flow and which one you put the gauge on? I've heard a
couple different ways, just wanted to get a popular opinion
Regards,
<http://www.firstdefensefire.com/>
E-mail message checked by Spyware Doctor (6.0.0.383)
Database version: 5.10760
http://www.pctools.com/en/spyware-doctor-antivirus/
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
------------------------------------------------------------------------
No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.169 / Virus Database: 270.7.1/1686 - Release Date: 9/23/2008 7:38 AM
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)