John

We use the appendix found in the International Fire Code for fire flow.
When a sprinkler system is utilized the Fire Code Official can reduce the
fire flow rate just never below 1500 gpm.  We have administratively reduced
it to zero on homes and buildings that are under 10,000 square feet.  

Let me know if you need more

Michael O'Brian 
www.inspector911.com
[EMAIL PROTECTED]

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John Luxford
Sent: Monday, September 29, 2008 5:12 PM
To: [email protected]
Subject: Fire Water Supply 

Forum,
              I have been advocating for dispensation of the fire hydrant
duty requirements when a building is fully sprinklered, properly designed
and installed.   My arguement is based on the fact that a response from F.B.
would be for clean-up, looking as the success stories in the past of fire
sprinklers and the safety afforded to the F.B. by the FS system.   Is this
(dispensation) applicable in the US - also I am surprised by the duty
required for the sprinkler system as posted  1500-2000USGPM is this for F.S
& Hydrant duty or only for ESFR in a big box application.
Regards from Down-Under.,
John Luxford.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to