What about pitching the lines and then heat tracing the mains and aux
drains per 8.16.4.1.3 (13 02ed)?
I don't think this is the best option but you were looking for
alternative ideas.
Dewayne

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Monday, September 29, 2008 4:00 PM
To: [email protected]
Subject: Alternate to pitch?

I visited a site the other day which consisted on 1.5 million sqft of
vacant industrial buildings built in the 1950's. The cost to heat these
building is astronomical and the owners are looking for cut costs. They
would like to convert the 30 +/- systems from wet to dry. 
Obviously the biggest obstacle is pipe pitch. Some of the lines appear
to pitch, but most lines and mains are flat (caveat: I have not gone in
with a level to check it, but rod lengths looked the same). The lines
look like they could be pitched, but the mains would be a challenge. Are
there any alternatives out there? I don't know of any, but I didn't know
if the collective mind had run across anything.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to