Hii. Thaanx for the quick replies. As Mr Todd guessed ,its a living quarters for workers and in Dubai we are following NFPA standards. The problem I face is that I had made my calculations for the sprinkler based on NFPA 13 and with occupancy hazard as Light Hazard. But our Client just crossed it :( and said its an Ordinary hazard Group 2. I checked NFPA ,But couldnt see such a thing. Have I missed something.??
Sam On Sat, Oct 25, 2008 at 5:23 PM, Todd Williams - FPDC <[EMAIL PROTECTED]> wrote: > Sam, > > Welcome aboard. By 'labour accommodations', I assume you mean living > quarters for workers. If so, then the occupancy would be Residential and > would need to be protected by either NFPA 13R or NFPA 13 Light Hazard, > depending on the arrangement of the building, local codes, etc. This, of > course, is under the assumption that Dubai is using the NFPA standards. > > > > At 03:34 AM 10/25/2008, you wrote: > >> Hi everyone. >> >> am a new kid on the block. >> >> a beginner to Fire protection Engineering and am working in Dubai. >> Found this forum as a very informative one >> >> I have a doubt regarding the occupancy hazard classification needed for >> labour accomodation. >> Labour accomodation is in portable cabins and is a G+1 Construction. >> >> >> >> Please give your valuable advice. >> >> sam >> _______________________________________________ >> Sprinklerforum mailing list >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum >> For Technical Assistance, send an email to: [EMAIL PROTECTED] >> >> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]> >> (Put the word unsubscribe in the subject field) >> > > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, Connecticut > www.fpdc.com > 860.535.2080 _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [EMAIL PROTECTED] > > To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]> > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [EMAIL PROTECTED] To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)