Hii
Thaanx  for the valuable response.

As most of you people said,Its the authorities demand and we have to do it
accordingly.Also I suppose its a case where we are providing better
protection rather than confining to the minimum reqd.
I have redesigned the system for Ordinary Hazard group 2 and got the
approval.
:)
anyway it was really helpful to have your views.

For Mr andrew-
It is under civil defence JAFZA.and its wasnt a fire hazard report.


Thaanxx again...

Sam
On Mon, Oct 27, 2008 at 2:42 PM, <[EMAIL PROTECTED]> wrote:

> Sam:
>
> In Dubai, the local authorities (not sure if you are under Civil Defense
> of JAFZA on this project) require a fire hazard report on most jobs.
> Included in this report is a classification of hazard of contents (light,
> ordinary and High per NFPA 101, 2007 edition, section 6.2.2).  I am
> curious if your customer is referring to this classification and not to
> the design density requirements for sprinklers (although you did say
> ordinary group 2 which would be sprinkler density).  Ordinary hazard of
> contents would not necessarily drive ordinary hazard sprinkler design. You
> may want to make sure the customer is referring to the right topic before
> you get to much further.  Also, with the nature of a lot of the labor
> housing facilities in Dubai, you may want to run the design requirements
> past the local AHJ.  The way some of those facilities are built and fenced
> in, the local authorities may have driven a higher design requirement (but
> I do not really suspect that they have).
>
> Andrew Weisfield
>
>
>
>
> David de Vries <[EMAIL PROTECTED]>
> Sent by: [EMAIL PROTECTED]
> 10/26/2008 08:25 PM
> Please respond to
> [email protected]
>
>
> To
> [email protected]
> cc
>
> Subject
> Re: Occupancy hazard for labour accomodation
>
>
>
>
>
>
> Sam:
>
>  Building on the prior comments and based on your client's expectations,
> perhaps your client does not understand the difference between "Ordinary
> Hazard" and "Light Hazard".  Sometimes clients need education and in this
> case, the economics favor the client and can make you look good.  That is,
> by your demonstration that a purely residential occupancy can be
> reasonably protected with a Light Hazard system or even a 13R system,
> which will save the client some money, you can end up looking like you
> have the client's interests at heart.
>
>  If on the other hand, the client selected an Ordinary Hazard system and
> that's what is truly wanted, that is what the client should get!
>
>  Good luck.
>
>  Dave
>
> Ron Greenman <[EMAIL PROTECTED]> wrote:
>  Sam,
>
> Reiterating what others have already said this building sounds like it
> could fall into the category of NFPA 13R which is less stringent than
> 13 light hazard. What the owner wants is what he gets. If you want a
> new Mercedes you don't expect the salesman to argue the merits the of
> a nice '98 Hyundai even if the latter meets your basic needs for
> transportation. This sounds like a common problem we discuss all the
> time on this Forum: You were given the work without adequate
> instruction, you did it with the customer's best interest in mind
> (typically that he wants to spend the least amount of money), and then
> he's dissatisfied because he didn't get what he expected even though
> he wasn't clear in telling you those expectations. My point is don't
> feel alone.
>
> On Sun, Oct 26, 2008 at 4:45 AM, John Drucker wrote:
> > Sam,
> >
> > Interestingly the 2002 NFPA-13 handbook commentary (11.2.1.3 pg 430)
> states
> > "Each hazard can be protected with the appropriate discharge criteria,
> or
> > the most demanding criteria can be used throughout the facility."
> >
> > Keep in mind that most building codes and reference standards are
> adequacy
> > requirements. Some use the word "minimum" but in reality its merely what
> the
> > consensus agree is necessary. Theres absolutely nothing restricting a
> > principal or stakeholder from stipulating something more then what a
> code or
> > standard requires with some exceptions. Density is one such area. We
> have
> > clients and engineers that stipulate OH-2 design for everything from
> > offices, restaurant service and seating areas, places of assembly and so
> > forth.
> >
> > In the context of whats acceptable from an AHJ's perspective, 2002
> NFPA-13
> > 5.2 provides that residential dwelling units are classified as light
> hazard
> > occupancies.
> >
> > Hope that helps,
> >
> > John Drucker
> > Fire Protection Subcode Official (AHJ)
> > Fire/Building/Electrical Inspector
> > New Jersey, USA
> >
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of sam b
> > Sent: Sunday, October 26, 2008 2:09 AM
> > To: [email protected]
> > Subject: Re: Occupancy hazard for labour accomodation
> >
> > Hii.
> > Thaanx for the quick replies.
> >
> > As Mr Todd guessed ,its a living quarters for workers and in Dubai we
> are
> > following NFPA standards.
> > The problem I face is that I had made my calculations for the sprinkler
> > based on NFPA 13 and with occupancy hazard as Light Hazard.
> > But our Client just crossed it :( and said its an Ordinary hazard Group
> 2.
> > I checked NFPA ,But couldnt see such a thing.
> > Have I missed something.??
> >
> > Sam
> >
> >
> >
> >
> > On Sat, Oct 25, 2008 at 5:23 PM, Todd Williams - FPDC wrote:
> >
> >> Sam,
> >>
> >> Welcome aboard. By 'labour accommodations', I assume you mean living
> >> quarters for workers. If so, then the occupancy would be Residential
> and
> >> would need to be protected by either NFPA 13R or NFPA 13 Light Hazard,
> >> depending on the arrangement of the building, local codes, etc. This,
> of
> >> course, is under the assumption that Dubai is using the NFPA standards.
> >>
> >>
> >>
> >> At 03:34 AM 10/25/2008, you wrote:
> >>
> >>> Hi everyone.
> >>>
> >>> am a new kid on the block.
> >>>
> >>> a beginner to Fire protection Engineering and am working in Dubai.
> >>> Found this forum as a very informative one
> >>>
> >>> I have a doubt regarding the occupancy hazard classification needed
> for
> >>> labour accomodation.
> >>> Labour accomodation is in portable cabins and is a G+1 Construction.
> >>>
> >>>
> >>>
> >>> Please give your valuable advice.
> >>>
> >>> sam
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>> For Technical Assistance, send an email to:
> [EMAIL PROTECTED]
> >>>
> >>> To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>>
> sprinkler.org>
> >>> (Put the word unsubscribe in the subject field)
> >>>
> >>
> >> Todd G. Williams, PE
> >> Fire Protection Design/Consulting
> >> Stonington, Connecticut
> >> www.fpdc.com
> >> 860.535.2080 _______________________________________________
> >> Sprinklerforum mailing list
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> For Technical Assistance, send an email to:
> [EMAIL PROTECTED]
> >>
> >> To Unsubscribe, send an email
> > to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>>
> sprinkler.org>
> >> (Put the word unsubscribe in the subject field)
> >>
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
> [EMAIL PROTECTED]
> >
> > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > For Technical Assistance, send an email to:
> [EMAIL PROTECTED]
> >
> > To Unsubscribe, send an email
> to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ron Greenman
> at home....
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> (Put the word unsubscribe in the subject field)
>
>
>
>
> This email is intended for named recipients only.
>  _______________________________________________
> Sprinklerforum mailing list
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> For Technical Assistance, send an email to: [EMAIL PROTECTED]
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]<[EMAIL PROTECTED]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to