Thank you guys! Great imput. I will call Tyco and the White paper was most
helpful.
Dennis
----- Original Message -----
From: "G. Tim Stone" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, November 13, 2008 10:01 AM
Subject: RE: Slippery Slope
Dennis,
I believe Chapter 8.3.1.1 of NFPA 13 2002 edition provides you with the
needed horse power to show that you are allowed to use Specific
Application
sprinklers
when shown that they can provide superior protection.
G. Tim Stone
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
TEL: (802) 434-2968 Fax: (802) 434-4343
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED] [mailto:sprinklerforum-
[EMAIL PROTECTED] On Behalf Of Dennis Browning
Sent: Thursday, November 13, 2008 12:10 PM
To: [email protected]
Subject: Slippery Slope
I have a project we designed the Dry System with 7 SD Attic heads. The
ME wants the Area and Slope increases per 11.2.3.2.4 and 11.2.3.2.5. I
pointed out the listing of the Attic heads but all he says is " If it's
OK with the Local AHJ, he takes " no exception to that design approach"
but he will not stamp the drawings saying this, even tho he DID stamp
the first set " rejected/ resubmit"!
LOcal AHJ requires plans to be stamped by the EOR or the Architect
prior to submission, and the Architect won't stamp them " because".
Trying to build a case that what we did is " per NFPA 13 and industry
standard.
Any thoughts?
Dennis Browning
Browning Fire
Medford, Oregon
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
--------------------------------------------------------------------------------
No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.175 / Virus Database: 270.9.2/1784 - Release Date: 11/12/2008
7:01 PM
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)