Two questions regarding the dissolution of the Light Hazard classification for 
Offices:

Are office buildings burning down because they were designed for Light Hazard? 
Are there any full scale fire tests that indicate the need to change Occupancy 
classification?

If the answer to either is yes, then ok..if not then why bother?

I am just curious because when the sprinkler criteria was changed and the 
minimum 7 psi was included for the listing and usage of residential heads, one 
of the prominent engineers in the country stated "it isn't like the buildings 
were burning down". I thought that was profound myself.

Greg McGahan
Operations Manager

Living Water Fire Protection
1160 McKenzie Road
P.O. Box 877
Cantonment, Florida 32533
(850) 937.1850 | Fax (850) 937.1852 | CellĀ (850) 554.3231
[EMAIL PROTECTED]



-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Tuesday, November 18, 2008 3:29 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa Existing 
PipeScheduledSystem Water Supply)

Agreed about the office thing.  Recent client wanted to try and convince me 
that they didn't need sprinklers in the office because their building was all 
concrete.  I said that's nice but a fire will most likely start INSIDE your 
concrete building unless you get hit by a meteor, which will probably still 
result in a fire inside.  I have noticed some jurisdictions requiring a minimum 
design criteria of .15 for office areas.  The Light hazard classification for 
office environments needs to go away. It's just not realistic when it comes to 
fuel loading and potential hazards.

In most industrial environments the chance for fire is usually far less than in 
most offices.  Reason being the factory environments have stricter rules on 
housekeeping and storage than most offices.  Don't see a lot of overloaded 
power strips in manufacturing plants either, boxes of rolled plotter paper on 
plastic, printer and copy machine toner, etc......

But we digress, back to the mechanical room...................

Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Chris Cahill
Sent: Tuesday, November 18, 2008 4:21 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa Existing 
PipeScheduledSystem Water Supply)

About the same funny as where I'm sitting right now and I suspect you are too.  
I'm a room with a lot of class III materials, stored up to 6' high, some in 
solid piles and harder to burn, some rolled paper easy to burn, about 20 lbs of 
exposed non-expanded plastics and about 5 lbs of non-exposed expanded plastic, 
more electrical violations than I like to admit but some how it's light hazard 
because I call it an office and our mech room is OH by tradition and few boxes 
of holiday decorations.  Maybe we should start calling mechanical room's 
offices. They are less hazardous than where I'm sitting even with the 
decorations.  With modern odd names and more from other cultures all electrical 
rooms are now labeled as Electa's office and the mechanical room is Phan's 
office.

BTW I've also just always done the OH thing in mech/electrical and let's throw 
in kitchens.

Also, thanks to those pointing out the mixed hazard stuff and 400 sq.ft.
Never noticed that before and I don't have a good or bad excuse.

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.

763-658-4483
763-658-4921 fax

Email: [EMAIL PROTECTED]

Mail: P.O. Box 69
        Waverly, MN 55390

Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
Sent: Tuesday, November 18, 2008 2:39 PM
To: [email protected]
Subject: RE: Mech/Electrical room classification (wa Existing Pipe 
ScheduledSystem Water Supply)

Mechanical room and no storage, now that's funny.

Where else is there to put all the holiday decorations and the last 10 years 
worth of business records, I mean like why let all that open space be wasted?

No way could I see any justification for either one of these rooms being 
considered LIGHT Hazard.

Must have been politicians that came up with that ruling.   ;)



Craig L. Prahl, CET
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark Sornsin
Sent: Tuesday, November 18, 2008 3:21 PM
To: '[email protected]'
Subject: RE: Mech/Electrical room classification (wa Existing Pipe 
ScheduledSystem Water Supply)

Oooh! Good one!

I my experience, we have done it that way out of tradition.  Maybe because 
electrical/mechanical rooms can be combined; many mechanical rooms have fuel 
fired equipment; both kinds of rooms often become storage rooms (rightfully or 
wrongly). If some engineer doesn't specify it, one can certainly argue in many 
cases that these rooms may not warrant protection beyond light hazard.
But I always spec them OH; as a contractor we designed them that way, too.

The ND members of this forum are all too familiar with the ND Dept of Health 
making them change their non-ordinary temperature heads to ordinary because 
"the mechanical room is really an air handling room with no storage and thus 
warrants light hazard protection and ordinary temp heads." Never mind the 
additional sprinklers, additional density, potential for future storage, and 
lack of human occupancy. "Those head must be changed!"

Mark Sornsin

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Tuesday, November 18, 2008 1:48 PM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply

Out of curiosity where do come up with electrical/mechanical rooms being OH?

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, November 18, 2008 11:15 AM
To: [email protected]
Subject: RE: Existing Pipe Scheduled System Water Supply

We need to be careful in our use of words here. This building is a light hazard 
occupancy.

All light hazard occupancy buildings will contain some areas of Ordinary 
hazard, such as kitchens laundry rooms, or electrical/mechanical rooms.
These areas do not change the classification of the hazard for the entire 
building, or the hose stream requirements.

While these areas must be protected per their specific hazard for density, if 
your largest OH II area is only 600 Sf then you only provide OH II density for 
that 600 SF area, and any smaller areas of the same hazard.
Usually this is done by reducing the spacing per head to like 75 Sf per head 
with 5.6K will give you 0.20 at just about 7 PSI. So for your 600 Sf you would 
calc 8 heads unless your Light hazard area required more than 8 heads, or was 
more remote, with the same number of heads.

Now because this was installed pipe schedule, you need to know if OH pipe 
schedule was used in the OH areas? Actually you need to Hydraulic the entire 
system to ensure the loss from the backflow will allow it to work per NFPA 13, 
2007 8.17.4.6.2.  But as far as your question goes "The Occupancy is Light 
Hazard" for the use of 11.2.2.1 so 15 Psi and the 30-60 Min.
duration
is OK.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



Timothy:

You must design for Ordinary Hazard in the Ordinary Hazard areas; Light in the 
Light Hazard Areas.  There is no "overall building design approach"; the 
building is not Light Hazard unless ALL areas of the building are light hazard.

Mark A. Sornsin, PE

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[EMAIL PROTECTED]

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to