I am currently designing in-rack sprinkler protection for an area
containing oil storage which falls under NFPA 30 (08ed).  One of the
requirements is 16.6.1.5 which states "If there are adjacent rack bays
that are not dedicated to storage of liquids, the barrier and in-rack
sprinkler protection shall extend at least 8 ft beyond the area devoted
to liquid storage.  In addition, adjacent racks across the aisles on
each side of the liquid storage shall be protected in accordance with
16.6.1."  16.6.1 is the fire protection design scheme for the in-racks
and barriers.  I take this to mean that we need to extend the liquid
storage criteria 8ft beyond the actual liquid storage in the same rack
and provide the same liquid storage protection criteria in adjacent
racks on both sides of the rack containing the storage even though no
liquid storage will take place.
The owner asked me if we only had to extend the protection 8ft within
the rack, why would we need protection in the adjacent racks if the the
aisles are 11ft wide?
He made a good point and the only answer I could give him was that it is
in the code.  Am I interpreting the fire protection requirements right?
Is there a distance for the aisle width in which sprinklers would not be
required for adjacent racks?
Thanks,
Dewayne  