Dewayne: 

Will the radiant heat from the racks only go straight across the aisles, or 
will it also travel in a straight line. but at a diagonal to the racks? 


Is the origin of this section FM. Is Joe H out there? 

Bruce Verhei 

----- Original Message ----- 
From: "Dewayne Martinez" <[EMAIL PROTECTED]> 
To: [email protected] 
Sent: Thursday, November 20, 2008 12:57:57 PM GMT -08:00 US/Canada Pacific 
Subject: Rack storage question 

I am currently designing in-rack sprinkler protection for an area 
containing oil storage which falls under NFPA 30 (08ed). One of the 
requirements is 16.6.1.5 which states "If there are adjacent rack bays 
that are not dedicated to storage of liquids, the barrier and in-rack 
sprinkler protection shall extend at least 8 ft beyond the area devoted 
to liquid storage. In addition, adjacent racks across the aisles on 
each side of the liquid storage shall be protected in accordance with 
16.6.1." 16.6.1 is the fire protection design scheme for the in-racks 
and barriers. I take this to mean that we need to extend the liquid 
storage criteria 8ft beyond the actual liquid storage in the same rack 
and provide the same liquid storage protection criteria in adjacent 
racks on both sides of the rack containing the storage even though no 
liquid storage will take place. 
The owner asked me if we only had to extend the protection 8ft within 
the rack, why would we need protection in the adjacent racks if the the 
aisles are 11ft wide? 
He made a good point and the only answer I could give him was that it is 
in the code. Am I interpreting the fire protection requirements right? 
Is there a distance for the aisle width in which sprinklers would not be 
required for adjacent racks? 
Thanks, 
Dewayne 
_______________________________________________ 
Sprinklerforum mailing list 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum 
For Technical Assistance, send an email to: [EMAIL PROTECTED] 

To Unsubscribe, send an email to:[EMAIL PROTECTED] 
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [EMAIL PROTECTED]

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to