2002 NFPA-13 11.2.3.3.1, 11.2.3.3.3, 11.2.3.3.4

John Drucker
Fire Protection Subcode Official (AHJ)
Red Bank, NJ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Saturday, November 22, 2008 11:22 AM
To: [email protected]
Subject: FW: subdivdied tenant spaces


I guess I have never ran into this exact situation before. 

Tenant buildout similar to a strip mall with mostly larger mall type stores
- Victoria's Secret, Brooks Brothers etc of 3,000-5,000 sq ft... Every unit
has its own control valve and is calculated individually. There are a few
small space that are tucked between the larger spaces - 4-7 heads with their
own control valve of course, 400-600 sq ft in area. All of the demising
walls are fire rated.

Should we calculate just the space or do we need to cross the fire walls to
get the required remote area.

Thanks for your help and NO the AHJ is not helpful....

Greg McGahan