The minimum pipe size has been 1" since 1940. There was only one piece of
3/4" in pipe schedule systems prior to 1940. Check the sizes again. Most
likely 1, 1, 1-1/4, 
1-1/2, 1-1/2, 2. Also check coverage - less than 100 sf/head for old
systems. Head types all old style?

Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
3300 King Ave
Cleveland, OH 44114
216-621-8899
216-570-7030 cell