The UFC doesn't explicitly address the area increase. However, it does
require the use of the building code for determination of allowable height,
area, construction type and use group. Therefore, if the sprinkler system
is used to gain an increase in allowable area, an NFPA 13 system is
required. This really only becomes an issue on dormitories, etc.
Christopher Born, P.E.
Clark Nexsen
Norfolk, VA
----- Original Message -----
From: "Phelps, Mark" <[email protected]>
To: <[email protected]>
Sent: Tuesday, January 06, 2009 6:47 PM
Subject: RE: another fire - this will be interesting
Do any of you guys have experience with the UFC (of military fame) as it
relates to this issue of area increases for sprinklers?
Mark at Aero
-----Original Message-----
From: [email protected]
[mailto:[email protected]]on Behalf Of George
Church
Sent: Tuesday, January 06, 2009 12:21 PM
To: [email protected]
Subject: RE: another fire - this will be interesting
I brought the same issue you up (story increase ok, no area increase except
with 13) in a design-build seminar at AFSA a couple years ago, mostly
because one of my competitors was in the room and I wanted him to know this
so at least maybe two of us would be high bidders.
Turned around to a room full of blank stares. Unless they remained quiet, no
one else knew this in a big seminar room. Glad they were there to learn, but
you'd have thought in a room full of folks forward-thinking enough to attend
seminars, no widespread knowledge of the IBC area increase.
So yup- residential, 4 stories or less, tire storage below....
glc
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Johnston
Sent: Tuesday, January 06, 2009 12:09 PM
To: [email protected]
Subject: RE: another fire - this will be interesting
This is very well put John,
The role of the FPE is starting to take off in my region a little slowly
though. One of my biggest struggles in the contracting world is if we are
competitively bidding a project against other sprinkler contractors that
don't know the Building and Fire Codes - they just operate on what NFPA
says. Example: an R Occupancy (3 story hotel) built beyond the allowable
area that the IBC allows, contractor A follows NFPA 13R because it's a
residential occupancy up to 4 stories - know big deal to him? However in
order to build the structure to the size that the owner would like it to be
the IBC requires the fire protection system be designed in accordance with
NFPA 13. We don't get the job because our price is too high and then the
local building code official doesn't catch it either - I have pointed this
out in the past to the AHJ - this particular AHJ had no idea that the intent
of the code wasn't being fulfilled. Unfortunately this happens too often in
our region. What is the fix? As much as I would like to see FPE's employed
by every jurisdiction this obviously won't happen due to budget issues. I
would like the other contractors to know what the IBC & IFC (or their state
adopted code) say's in order accomplish the originally intended scope of
work, being that these codes are law and NFPA is a guide on how to fulfill
the law.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]
-----Original Message-----
From: John Drucker [mailto:[email protected]]
Sent: Tuesday, January 06, 2009 6:46 AM
To: [email protected]
Subject: RE: another fire - this will be interesting
Simply put "fire protection" is not seamless. Often enough it's a
patchwork of pieces and parts assembled without a clear and common
objective. We see this everyday with smoke detectors being installed in
unsprinklered elevator hoistways because no one told the alarm engineer
that sprinklers had been eliminated by the sprinkler engineer, or fire
dampers installed in one hour walls in fully sprinklered buildings
because no one told the mechanical engineer. The disconnect with the
fire service is yet another example, site planning left to the civil
engineer without regard to fire protection needs.
What we need are MEPF firms, engineering firms that employ and fully
utilize fire protection engineers to look at the big picture, assess,
plan, design, coordinate and supervise cost effective and efficient fire
protection solutions.
If as a fire protection engineer you're simply designing fire alarm or
sprinkler systems you are not working to your full potential ! There
are firms that provide life safety analysis to provide passive fire
protection solutions, often coined working for the "dark side" they
nonetheless do what others are not, looking at the big picture. High
rise sprinklers in Chicago or San Diego anyone ?
So how does the active fire protection community counter this claim,
perhaps by long term planning, synergistic value driven engineering. It
goes all the way back to codes and standards, how many cycles did it
take to recognize sprinklers in fully sprinklered buildings for
notification survivability on fire alarm systems ?
One stop shopping ladies and gentlemen, one stop shopping.
Sincerely
John Drucker
Fire Protection Subcode Official (AHJ)
Building/Fire/Electrical Inspector
Safe Buildings Save Lives !
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris
Cahill
Sent: Monday, January 05, 2009 10:36 AM
To: [email protected]
Subject: RE: another fire - this will be interesting
Ron said "(I suspect the savings in mains, hydrants, fire stations,
apparatus and firefighters is way more than a wash in fully sprinklered,
planned communities than the cost of sprinklering schools)."
Were these savings realized? Last I read which was a long time ago
there was very little saved on the reduction in the list you provided.
They never actually followed through in reducing mains and limiting
stations etc. I will certainly say in the macro scale these saving are
not being fully realized. Hell we still have fully paid stations in
many departments that average < 1 call a day and plenty more that are <
2. As a pay-per-call volunteer I saw more fire than many paid guys in
these parts.
Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
763-658-4483
763-658-4921 fax
Email: [email protected]
Mail: P.O. Box 69
Waverly, MN 55390
Location: 4439 Hwy 12 SW
Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
Sent: Friday, January 02, 2009 2:05 PM
To: [email protected]
Subject: Re: another fire - this will be interesting
Good point so far overlooked. There's also the dubious "saved
foundation" success that may have not been worth the risk of going into
harm's way. And no one has brought up the environmental advantages of
sprinklers--less smoke, less destroyed building materials to dispose of,
less dirty water to process and, of course, less water used overall. And
the Scottsdale less public money spent on firefighting infrastructure (I
suspect the savings in mains, hydrants, fire stations, apparatus and
firefighters is way more than a wash in fully sprinklered, planned
communities than the cost of sprinklering schools).
On Fri, Jan 2, 2009 at 11:49 AM, Dave <[email protected]> wrote:
Since we are offering up various thoughts and theories on the general
application of sprinklers ..... Regardless of how much egress time is
allegedly available or occupant ability to respond or even construction
materials & methods - there still is a fire in a building - Presuming
we get everyone out safely and that eliminates the 'life safety need for
sprinklers' will we then NOT call the fire department to respond??
Once there's a fire in a building there is another completely real
life
hazard in play - the responding emergency personnel. Some may enter the
building and be very close to harm's way and others may respond and have
ancillary functions - traffic control, EMS, crowds etc. Regardless of
the specifics we can generally agree that a fire in a non-sprinklered
building will be larger than the same fire in a sprinklered building.
It's not always the fire but medical emergencies or trips & falls that
create the threat of harm. The larger the fire the greater its duration
and intensity
- all of which increase exposure and life safety risk to responders.
Personally I don't get behind the non-combustible and limited or low
fuel
load argument as a valid application of sprinkler omission. Maybe thats
just my narrow focus or perhaps its because I've been to alot bigger
fires in non-sprinklered buildings than sprinklered buildings. The
closer you get to the gun - the bigger the bullet.
Thanks & Happy New Year
Dave P.
Fireman first and always.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]
To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]
To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to:
[email protected]
To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity
to which it is addressed and may contain information that is privileged and
confidential, nor is it, unless specifically stated, intended to be relied
upon by any person or persons other than the individual or entity named
above and no warranties or representations are made or intended to persons
or entities not named above. If the reader is not the intended recipient,
you are hereby notified that any dissemination, distribution or copying of
this communication is strictly prohibited. If you have received this
communication in error, please notify us immediately by telephone, return
this message to the address above and delete all copies. Thank you.
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)