Hello Chris, We use a high volume air compressor starting at about 50 PSI, Walk around and listen for the "Whistle" of the leak, If not found increase the air pressure and walk it again. WATCH the air pressure and slowly increase it between walks. Depending on the age of the system and what the pipe looks like inside how high they limit the pressure to. Yes you might cause a few more small leaks to appear but the disclaimer we have the customer sign first contains wording to allow repair of those at the customers expense also.
Wednesday, January 7, 2009, 10:09:32 AM, you wrote: > Any tips on tracking down leaks that are buried in insulation and enclosed > in wall and ceilings? We suspect the system isn't sloped properly and > doesn't have drains. We don't want to fill it with water and wait for the > wet spots. Seems like too much future liability. We did an identical > building a few years later and went anti-freeze because we weren't smart > enough to figure out how to grade the system and deal with future dry > issues. Guess we aren't smarter today inheriting someone else's dry system. > > Chris Cahill, P.E. > Fire Protection Engineer > Sentry Fire Protection, Inc. > > 763-658-4483 > 763-658-4921 fax > > Email: [email protected] > > Mail: P.O. Box 69 > Waverly, MN 55390 > > Location: 4439 Hwy 12 SW > Waverly, MN 55390 > > _______________________________________________ > Sprinklerforum mailing list > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > For Technical Assistance, send an email to: [email protected] > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) -- Best regards, Charles Thurston mailto:[email protected] Coastal Fire Protection _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)