CPVC can be installed in an exposed environment but with specific guidelines such as being flush to ceiling, sprinkler spacing and flat smooth ceiling, etc.. If you were using hip style sprinklers that tells me the construction of your attic doesn't meet these guidelines, so no.
Russell Rewis Brown Automatic Sprinklers, Inc. 107C Hemlock Street Valdosta, Georgia 31601 229-244-8130 [email protected] "?Can?CPVC piping be run in an attic space using SSU/SSP in a NFPA-13 type system? I We were using Tyco Attic HIP heads originally, but are unable due to the wood member changes. George Medina Jr." _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)