George,
I believe the only way you can run cpvc supplying pendants in a attic that
requires sprinklers is by using "attic" sprinklers fed from steel pipe and
then the cpvc pipe will need to be thermally (fire not cold) protected with
insulation 6" above and 12" to each side of the pipe.  Check the Tyco data
sheets though.

Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
[email protected]


-----Original Message-----
From: George Medina Jr [mailto:[email protected]] 
Sent: Wednesday, January 21, 2009 5:05 PM
To: [email protected]
Subject: CPVC in Sprinklered attic space

?Can?CPVC piping be run in an attic space using SSU/SSP in a NFPA-13 type
system? I We were using Tyco Attic HIP heads originally, but are unable due
to the wood member changes.


George Medina Jr.