George, I believe the only way you can run cpvc supplying pendants in a attic that requires sprinklers is by using "attic" sprinklers fed from steel pipe and then the cpvc pipe will need to be thermally (fire not cold) protected with insulation 6" above and 12" to each side of the pipe. Check the Tyco data sheets though.
Jim Johnston, P.E. Fire Protection Engineer Inland Fire Protection, Inc 1100 Ahtanum Road Yakima, WA 98903 Phone 509-248-4471 Fax 509-248-1180 [email protected] -----Original Message----- From: George Medina Jr [mailto:[email protected]] Sent: Wednesday, January 21, 2009 5:05 PM To: [email protected] Subject: CPVC in Sprinklered attic space ?Can?CPVC piping be run in an attic space using SSU/SSP in a NFPA-13 type system? I We were using Tyco Attic HIP heads originally, but are unable due to the wood member changes. George Medina Jr. _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)