Different critters all together.   Soft start and stop electronically powers 
the pump up and down in millisecond pulses that prevent a full hit of locked 
rotor current on start up or the hammering effect of an instant-off stop, both 
electrically and hydraulically.   Variable speed drives ramp the driver up or 
down in engine speed in response to demand, so if only a couple sprinklers or 
one hose valve are open, there's less pump output than if there was a huge 
demand downstream of the pressure sensing device.   The VSD works at a "set 
pressure" (new definition), which is the residual that the equipment maintains 
as it ramps the flows up or down with demand.   

One feature works at the very beginning and/or end of a run cycle, and the 
other one during the cycle.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Randy Knutson
Sent: Monday, February 02, 2009 4:04 PM
To: [email protected]
Subject: RE: - prescriptions against soft-start pumps in NFPA watersupplies..

What's the difference between a soft start and a variable Frequency drive
controllers? VFD's are allowed per NFPA 20.

Randy
Shilo Automatic Sprinkler, Inc.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of å... ....
Sent: Sunday, February 01, 2009 3:40 AM
To: [email protected]
Subject: - prescriptions against soft-start pumps in NFPA water supplies..

NFPA 20 & 24

water supply pumps and supply systems.


We have 3 large pumps drawings from a large reservoir.
water supply is devoted to a campus of buildings.
these are large volume pumps,  redundant.

Is there an NFPA requirement that these
large pumps can NOT be soft start?
We have predictions of water hammer,
and wish to avoid this via soft start.

scot deal
excelsior fire engineering
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 3820 (20090203) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus signature 
database 3820 (20090203) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to