8.16.2.6 Discharge of Drain Valves.
8.16.2.6.1* Direct interconnections shall not be made between
sprinkler drains and sewers.
8.16.2.6.2 The drain discharge shall conform to any health or
water department regulations.
8.17.4.1* Main Drain Test Connections.
8.17.4.1.1 Main drain test connections shall be provided at
locations that will permit flow tests of water supplies and connections.
8.17.4.1.2 They shall be so installed that the valve can be
opened wide for a sufficient time to assure a proper test without
causing water damage.
8.17.4.1.3 Main drain connections shall be sized in accordance

If the drain won't handle the main drain flow it's a pretty good bet you'll
cause water damage.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thomas
Reinhardt
Sent: Wednesday, February 04, 2009 10:40 AM
To: [email protected]
Subject: Main Drain on sprinkler system.

Is there anything in the code that says the drain on the floor must be able
to handle the full flow of the 2inch main drain? Plenty of times the drain
can't handle the flow when a main drain test is performed.
Thanks

 

Tom Reinhardt

Wheeling Fire Inspector

255 W. Dundee

Wheeling,IL 60090

phone 847-459-2669

 

 

 

 


_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to