2007 NFPA13 8.16.2.4 is concerned with system, main drain, or sectional and
in this section 8.16.2.4.4. states such a requirement that you speak of;
however, to me the wording implies the act of draining and not drain testing
but logic might lead one to not want to stand in two feet of water though.

Russell Rewis
Brown Automatic Sprinklers, Inc.
107C Hemlock Street
Valdosta, Georgia 31601
229-244-8130
[email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thomas
Reinhardt
Sent: Wednesday, February 04, 2009 12:40 PM
To: [email protected]
Subject: Main Drain on sprinkler system.

Is there anything in the code that says the drain on the floor must be
able to handle the full flow of the 2inch main drain? Plenty of times
the drain can't handle the flow when a main drain test is performed.
Thanks

 

Tom Reinhardt

Wheeling Fire Inspector

255 W. Dundee

Wheeling,IL 60090

phone 847-459-2669

 

 

 

 