Yep SCH 80... From Wilki..

pipe size (IPS) is an older system still used by some manufacturers and
legacy drawings and equipment. The IPS number is the same as the NPS number,
but the schedules were limited to Standard Wall (STD), Extra Strong (XS),
and Double Extra Strong (XXS). STD is identical to SCH 40 for NPS 1/8 to NPS
10, inclusive, and indicates .375" wall thickness for NPS 12 and larger. XS
is identical to SCH 80 for NPS 1/8 to NPS 8, inclusive, and indicates .500"
wall thickness for NPS 8 and larger. Different definitions exist for XXS,
but it is generally thicker than schedule 160.

R/
Matt

Matthew J. Willis
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-387-1163 Facsimile
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Knight
Sent: Friday, February 13, 2009 1:40 PM
To: [email protected]
Subject: Steel Piping and Tanks


Back to NFPA 22 again today.  Section 13.1.15.2.2 states that "steel pipe 2"
to 5" shall be extra-strong weight".
I am assuming that this means at least schedule 40.  Is my assumption
correct?

Thanks,

Bob Knight, CET
(208) 318-3057
[email protected]
www.firebyknight.com


No virus found in this outgoing message.
Checked by AVG - www.avg.com
Version: 8.0.233 / Virus Database: 270.10.23/1951 - Release Date: 02/13/09
06:51:00

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to