In the smaller pipe sizes that you reference extra strong (XS) pipe is
schedule 80. Schedule 40 is standard weight pipe.
John Hoffman P.E. | Fire Protection Engineer | Burns & McDonnell
Engineering | 2000 E. 95th St | Kansas City, MO 64131 | ph 816-997-7213
"Bob Knight"
<b...@firebyknight
.com> To
Sent by: <[email protected]>
sprinklerforum-bo cc
un...@firesprinkl
er.org Subject
Steel Piping and Tanks
02/13/2009 01:40
PM
Please respond to
sprinklerfo...@fi
resprinkler.org
Back to NFPA 22 again today. Section 13.1.15.2.2 states that "steel pipe
2"
to 5" shall be extra-strong weight".
I am assuming that this means at least schedule 40. Is my assumption
correct?