I agree. In the 02 edition see 9.3.5.1.2. I could not find any examples online. It sounds like the roof system may be designed for loads creating a downward type stress. An engineering review will be needed to determine if the stresses created underneath and pushing upward can be handled. Also for hanging do not forget 9.2.1.3.1 also from the 02.
R/ Matt Matthew J. Willis Norred Fire Systems L.L.C. 318-387-1134 Voice 318-387-1163 Facsimile [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Monday, March 16, 2009 9:24 AM To: [email protected] Subject: RE: Bahlen Roof System Go directly to the structural engineer responsponsible for the roofing system and get written clarification on hanging and bracing. I wouldn't do anything unless I had directions in writing. Craig L. Prahl, CET Fire Protection Specialist Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [email protected] http://www.ch2m.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jimmy Waite Sent: Monday, March 16, 2009 10:10 AM To: [email protected] Subject: Bahlen Roof System Good morning everyone. I am starting to work on a project, and I would like to ask your advice. We just got a job retro-fitting a building in an earthquake zone. One area of the building has a "Bahlen Roof System" (when I googled, I came up with Behlen, if that helps). The point of the roof system is to create large open spaces without needing columns. This particular roof system is a convex roof, but the finished ceiling is horizontal. I think there is a mess of wires, tension cables, and what not that are skinned with a fairly heavy duty sheet metal. My concern is not so much with hanging our system, but with bracing it. Has anyone else dealt with a roof system like this? I would like to hear from some of you before I contact the manufacturer. Their website is pretty generic, and the roof system page is under construction (go figure). Thanks in advance, Jimmy Waite Burtell Fire [email protected] 406-652-7697 _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)