How is it that you have the test meter hooked up to city water?   

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 




-----Original Message-----
From: George Medina Jr [mailto:[email protected]]
Sent: Wednesday, March 18, 2009 2:04 PM
To: [email protected]
Subject: Check Valve On Discharge side of Flow Meter

NFPA No.:Z4Pump02 page 108 - States that a check valve is required on the 
discharge side of flow meter. Our union field guys state they never put one 
on?there. Is this correct?
I believe a flow meter would be damaged from positive city pressure back 
flowing through the meter after shutting down the pump and before closing the 
isolation valve. Somebody correct me for being wrong.


George Medina Jr.
Sr. Fire Sprinkler Designer
Dorvin D. Leis Inc.
Honolulu, HI 96819

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to